PDA

View Full Version : XSY-AT1 VFD on/off and speed wiring enquiry



marbles
30-07-2018, 11:16 AM
Hi,

I recently bought a XSY-AT1 VFD (1ph to 3ph) to run my 2.2kw air spindle as part of a new machine build. I'd like it to start stop, and if possible also set the speed from Mach3 gcode. Its not clear to me from the wiring diagrams of the VFD which control wiring connections to connect to the BOB. Any thoughts or links welcome.24607

Jeroen Zeemeijer
05-11-2018, 11:17 AM
Hi,

I recently bought a XSY-AT1 VFD (1ph to 3ph) to run my 2.2kw air spindle as part of a new machine build. I'd like it to start stop, and if possible also set the speed from Mach3 gcode. Its not clear to me from the wiring diagrams of the VFD which control wiring connections to connect to the BOB. Any thoughts or links welcome.24607

Hi Marbles,

In order to control both speed and direction you preferably need to have a 0-10V or 0-5V output on your BOB along with one or two relay outputs for direction control. XSY-AT1 VFD also supports 4-20 mA input signal but this is less common for DIY projects. However for longer wire distance a better option since voltage drop is less of an issue.

The analogue voltage signal connects to the COM (-) and VL1 (+) terminal from the top of the VFD. Also you need to adjust setting P10 (working frequency source) to setting 2 to make this work. This will control spindle speed from min rpm to max rpm set in your VFD.
For direction control a relay output from BOB is used and connected in series between terminal X5 and COM on VFD. This is making the spindle run backwards when active. Depending on your needs this could be enough to control your spindle. Another option is to use terminal X5 (run in reverse) or X3 (swap direction of spindle rotation). So in my opinion just 1 relay should be enough in this case.

Main external control settings:

P10 frequency source setting (2) // external command
P11 start/stop setting (2) // external command like switch or relay (also activates direction control)
P65 start-up state VFD (this adjust the common state of your VFD after start-up) eg. Forward/ Reverse / other.
P50 can be set to 8. This makes terminal X1 your (reset VFD) input.

Good luck,

Jeroen

marbles
05-11-2018, 01:01 PM
Good luck,

Jeroen

Thanks Jeroen! I got there in the end with the wiring so it starts and stops. The programming of the VFD I found harder and im still not convinced i've set the perameters 100% correctly.

roadline
28-01-2019, 03:41 AM
Hi marbles,
I'm new here, need help. I had the same problem setting up my spindle using xsy-at1vfd. I've already set the given parameter but my spindle doesn't turn. My vfd response to the signal from mach3. It changes frequency once I change the spindle rotation but the motor has no response. Looks like there was power transmitted to the motor. I'm kinda confused on the wiring (eg. Relay output on Bob and connected in series between X5 and COM.) does this means that I have to connect the two relay terminal on my BOB? And connect it to the X5 and COM(shorted as per vfd manual)

Alex61
08-03-2019, 01:28 PM
Hi

I have an XSY-AT1 unit to work a 2.2kw three phase motor from a single phase supply. I have wired it up correctly and can only get 230v across the phases instead of 380v to 440v ? Any ideas if I have wired it wrong please assist

tmcgree
29-04-2019, 06:07 PM
Hi all,
I recently purchased a XSY-AT1 VFD, and am having some problems -I was hoping you can help.
I saw a number of videos of guys using these on Youtube so figured it was worth a shot since my application is simple and the price was good.
I am driving a Baldor 2HP 3Ph motor with it and have a single phase input (220V) on the VFD. I have it all wired up as it should be, but as I turn the potentiometer, the motor starts to turn but with allot vibration, especially at low frequencies I can see and hear the motor bumping with every cycle. It seems as though the three phases are unbalanced somehow. I checked as best I could with a multi-meter on each wire to the motor and all three signals seem to be there, appear to be pretty identical. (with respect to each other and to ground).

As a test I took the motor and hooked it up to a Hitachi VFD I was already using for my lathe and it ran perfectly smoothly all the way down to 1 Hz. So the motor is fine.

At first I thought the problem might have to do with the default frequencies being 50HZ as my motor specifies 60Hz. So, I changed each frequency parameter on the VFD to 60Hz (also intermediate frequencies to 30Hz) but this did not help.
It seems pretty clear that there is something I am not understanding or perhaps I have a defective unit.

Any suggestions you have would be very welcome.


Tom McGreevy

Lee Roberts
29-04-2019, 07:33 PM
Don't know if this will help much but here is the install/instructions for the XSY-AT1 VFD Inverter.

I'm going to ask Steve Jordan (https://www.youtube.com/channel/UCEpeQtxhVUTtMZzBpdegp-w) to pop in on this thread and see if he can help, I know he did an upgrade to a mini lathe using this unit.

Sorry I cant help more guys.

tmcgree
29-04-2019, 07:39 PM
Thanks Lee,
I have the manual already and I did post the question to Steve Jordon on his youtube channel, but he never responded - I'm not sure if he ever noticed it though - he looks pretty busy.

marbles
29-04-2019, 09:40 PM
Hi all,
I recently purchased a XSY-AT1 VFD, and am having some problems -I was hoping you can help.
I saw a number of videos of guys using these on Youtube so figured it was worth a shot since my application is simple and the price was good.
I am driving a Baldor 2HP 3Ph motor with it and have a single phase input (220V) on the VFD. I have it all wired up as it should be, but as I turn the potentiometer, the motor starts to turn but with allot vibration, especially at low frequencies I can see and hear the motor bumping with every cycle. It seems as though the three phases are unbalanced somehow. I checked as best I could with a multi-meter on each wire to the motor and all three signals seem to be there, appear to be pretty identical. (with respect to each other and to ground).

As a test I took the motor and hooked it up to a Hitachi VFD I was already using for my lathe and it ran perfectly smoothly all the way down to 1 Hz. So the motor is fine.

At first I thought the problem might have to do with the default frequencies being 50HZ as my motor specifies 60Hz. So, I changed each frequency parameter on the VFD to 60Hz (also intermediate frequencies to 30Hz) but this did not help.
It seems pretty clear that there is something I am not understanding or perhaps I have a defective unit.

Any suggestions you have would be very welcome.


Tom McGreevy

Wish I could assist Tom. I had a similar problem and found the spindle wiring to be incorrect but you already know the correct wiring so its not that. the First port of call sounds like an investigation to determine if there a fault, but you know that already.

Lee Roberts
11-09-2019, 11:20 PM
Hi,

For anyone looking for a known set of working parameters/settings for the XSY-AT1 VFD, George (tarawa (http://www.mycncuk.com/members/25219-tarawa)) has posted back his settings that worked for him, the link to this info is below:

Link: Generic Chinese VFD, XSY-AT1 Programming Parameters/Settings (http://www.mycncuk.com/threads/12842-Generic-Chinese-VFD-XSY-AT1-Programming-Parameters-Settings)

taths
13-11-2019, 10:12 PM
hi efstathios greece
to run my 2.2kw water spindle as part of a new machine build. start stop,it worked very well and if possible also set the speed from Mach3 gcode. Its not clear to me from the wiring diagrams of the VFD which.
I used parameters/settings for the XSY-AT1 VFD, George (tarawa)

Machifit NVCM /6 Axis CNC Controller MACH3 USB
Minleaf AT1-2200X 2.2KW 220V PWM Control Inverter 1Phase Input 3Phase Out Inverter Variable Frequency Inverter26734

Jay2182
05-02-2020, 11:39 AM
Hi can some1 help me setting my inverter? the acceleration and speed ect. for my plastering machine plssss
https://youtu.be/DyEAEZMtDQw?t=11

Luciano
11-08-2020, 07:08 AM
Buongiorno ragazzi..mi trovo davanti ad un problema per me abbastanza grosso..premetto che di inverter non ci capisco nulla.
Ho acquistato questo inverter XSY-AT1..e devo configurare con il mio tornio DamatoMacchine.il suo motore è un 220V x 750w 50Hz cioè monofase e la corrente di casa e 220v...ho provato spulciando in rete ma non ha portato nessun risultato..chi mi può dare l'esatta sequenze di impostazioni.con manuali.in anticipo grazie.

// TRANSLATION // Lee
Hello guys .. I am faced with a problem that is quite big for me .. I presume that I do not understand anything about the inverter. I purchased this XSY-AT1 inverter .. and I have to configure it with my DamatoMacchine lathe. Its motor is a 220V x 750w 50Hz that is single-phase and the house current is 220v ... I tried sifting through the network but it didn't bring any results ..who can give me the exact sequences of settings. with manuals. in advance thanks.

Clive S
11-08-2020, 09:21 AM
Buongiorno ragazzi..mi trovo davanti ad un problema per me abbastanza grosso..premetto che di inverter non ci capisco nulla.
Ho acquistato questo inverter XSY-AT1..e devo configurare con il mio tornio DamatoMacchine.il suo motore è un 220V x 750w 50Hz cioè monofase e la corrente di casa e 220v...ho provato spulciando in rete ma non ha portato nessun risultato..chi mi può dare l'esatta sequenze di impostazioni.con manuali.in anticipo grazie.

// TRANSLATION // Lee
Hello guys .. I am faced with a problem that is quite big for me .. I presume that I do not understand anything about the inverter. I purchased this XSY-AT1 inverter .. and I have to configure it with my DamatoMacchine lathe. Its motor is a 220V x 750w 50Hz that is single-phase and the house current is 220v ... I tried sifting through the network but it didn't bring any results ..who can give me the exact sequences of settings. with manuals. in advance thanks.

Is this what you are looking for https://www.youtube.com/watch?v=uMTb7uy1HfU

maxivariador
07-12-2021, 01:04 PM
alguien sabe como emplear la comunicacion rs 485 de este modelo de variadores .y el lenguaje que se emplea si es hexdecimal binario etc.....un saludo

Translation by Lee

"someone knows how to use the rs 485 communication of this model of drives. and the language that is used if it is hexdecimal binary etc ..... a greeting"

any0n
10-03-2022, 12:47 AM
...
"someone knows how to use the rs 485 communication of this model of drives. and the language that is used if it is hexdecimal binary etc ..... a greeting"

Folks, for posterity (and hoping someone can help), here's some info on getting through to XSY-AT* VFD using Modbus ASCII protocol: https://www.chipmaker.ru/topic/218090/?do=findComment&comment=4791765

I've written a little python program, but so far I've got only random garbage back (padded with lots of zeros) from the serial port, regardless of what command I send and baud rate used. The VFD works fine using panel controls.



# send the "jog" command
# ./send-cmd.py '3A 30 31 30 36 32 30 30 30 30 30 30 33 44 36 0D 0A'
ascii: 3A 30 31 30 36 32 30 30 30 30 30 30 33 44 36 0D 0A hex: bytearray(b':010620000003D6\r\n')
response: [192, 236, 214, 246, 54, 182, 246, 246, 246, 246, 246, 246, 150, 118, 77, 229, 235]


Hope someone has figured it out and can help..