Page 1 of 2 12 LastLast

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    You have the BOB 12V pin connected to the 10V output pin on the VFD. This definitely looks wrong. No connection needed here.

    Otherwise, analogue out and ground pins look fine. From the data you give, it looks as if you have configured the VFD for 0-5V speed input, which is correct for that BOB.

    As m-c says, that analogue signal is just for speed control. You also need at least one connection from a digital output pin on the BOB to one of DI1-6 on the VFD. The VFD manual should tell you which pin but these can often be reconfigured. Look for an input called something like Run. There will probably also be an input marked For/Rev. However, sometimes these are configured as two pins, one for forwards and one for reverse. For normal router use, you can forget reverse as you only want to run the spindle in the forwards direction. So, you need the analogue signal to set the speed and the digital signal to turn the VFD on.

    What software are you using to drive this - Mach3? This will also need to be configured to generate the right signals from the BOB.

  2. The Following User Says Thank You to Neale For This Useful Post:


  3. #2
    Quote Originally Posted by Neale View Post
    You have the BOB 12V pin connected to the 10V output pin on the VFD. This definitely looks wrong. No connection needed here.

    Otherwise, analogue out and ground pins look fine. From the data you give, it looks as if you have configured the VFD for 0-5V speed input, which is correct for that BOB.

    As m-c says, that analogue signal is just for speed control. You also need at least one connection from a digital output pin on the BOB to one of DI1-6 on the VFD. The VFD manual should tell you which pin but these can often be reconfigured. Look for an input called something like Run. There will probably also be an input marked For/Rev. However, sometimes these are configured as two pins, one for forwards and one for reverse. For normal router use, you can forget reverse as you only want to run the spindle in the forwards direction. So, you need the analogue signal to set the speed and the digital signal to turn the VFD on.

    What software are you using to drive this - Mach3? This will also need to be configured to generate the right signals from the BOB.

    Neale,

    Thank you for your reply.

    I assumed that the +10v shall be provided from external source. Thank you for clarification on that :) I have disconnected wire that goes from +12Vout to VFD.

    The software I use is UCCNC (purchased together with UC300 motion controller), and spindle settings are:

    Click image for larger version. 

Name:	VFD_UCCNC_settings.JPG 
Views:	572 
Size:	36.8 KB 
ID:	19263


    once M3S24000 is given through UCCNC app - the VFD shows close to 400hz (the voltage from analog out is not 5v however (4.5 approx)).

    Click image for larger version. 

Name:	2016-09-24 10.05.26.jpg 
Views:	914 
Size:	193.1 KB 
ID:	19264


    The bad thing is that for DI control I need 24V power supply.. I thought I will get away with 12 + 5 (HDDB2 needs 12V, UC300 needs 5V). But looks like not :) :)

    Than the question is from where in the BOB i shall take digital signal for "start" "stop" signal, or maybe than it is possible to have forward and reverse control too (I know that VFD as capable doing so, but where to get signals to control that) ?
    I have 3 AM882 connected to BOB and 1 output is free to use - can I use this as my "digital outputs" to VFD ? :

    Click image for larger version. 

Name:	Screen Shot 2016-09-24 at 10.17.01.png 
Views:	1720 
Size:	1.54 MB 
ID:	19265
    Click image for larger version. 

Name:	Screen Shot 2016-09-24 at 10.16.36.png 
Views:	712 
Size:	103.0 KB 
ID:	19266


    Thank you

    TM

  4. #3
    I have been having a look at the relevant manuals. Good news is that the BOB and the VFD inputs are compatible and you do not need any additional power supply. The installation manual, p48 in the copy I found, shows that there is a switch which will let you do this. See "Sink position using the output power supply for the digital inputs". The BOB outputs have a voltage and current rating that should be fine. Set the switch as shown in the diagram, and connect e.g. BOB pin 26 (output 1, LPT port 17) to the appropriate VFD DI pin.

    Next job is to configure (or check) that the VFD DI pins are correctly set up. The pins are programmable - see Programming Manual p125 onwards. You should start by checking how these are currently set but I would guess that from the factory a couple of these pins are set to For and Rev by default. You will need to check the manual to find out how to read a parameter and then modify it if needed.

    That's a start - I'm afraid that I don't have time to read the manual in great detail but I hope that that points you in the right direction. Overall, it looks as if everything should work fine once you have the correct pins connected and the VFD configured.

    Good luck!
    Last edited by Neale; 24-09-2016 at 05:17 PM.

  5. #4
    Quote Originally Posted by Neale View Post
    I have been having a look at the relevant manuals. Good news is that the BOB and the VFD inputs are compatible and you do not need any additional power supply. The installation manual, p48 in the copy I found, shows that there is a switch which will let you do this. See "Sink position using the output power supply for the digital inputs". The BOB outputs have a voltage and current rating that should be fine. Set the switch as shown in the diagram, and connect e.g. BOB pin 26 (output 1, LPT port 17) to the appropriate VFD DI pin.

    Next job is to configure (or check) that the VFD DI pins are correctly set up. The pins are programmable - see Programming Manual p125 onwards. You should start by checking how these are currently set but I would guess that from the factory a couple of these pins are set to For and Rev by default. You will need to check the manual to find out how to read a parameter and then modify it if needed.

    That's a start - I'm afraid that I don't have time to read the manual in great detail but I hope that that points you in the right direction. Overall, it looks as if everything should work fine once you have the correct pins connected and the VFD configured.

    Good luck!

    Neale,

    thank You once more for directions. Much appreciated.

    with your help I got spindle to run :)

    Here is my wiring at he moment:

    Click image for larger version. 

Name:	Wiring spindle (rev02).JPG 
Views:	1764 
Size:	53.6 KB 
ID:	19284

    Output 4 and Analog Output are activated together (PIN 16)
    Output 3 are set as Dir in UCCNC software, activated with PIN 14.

    I have managed to connect and use Output #3 as Direction signal. Settings in UCCNC:

    Click image for larger version. 

Name:	UCCNC settings for spindle.jpg 
Views:	681 
Size:	77.2 KB 
ID:	19285

    Here is short video from the test:



    However I have few problems so far:

    1. When spindle is activated with "forward" signal (M3S24000), spindle goes up to speed and handles speeds down to approx M3S1000). The problem is with reverse - it goes up to speed all good with M4S24000, but once speed set to 12000 spindle stops. It is the same if I would try to start spindle with lower speed than 15000 - spindle just wont start. Sometimes this happens with FWD too.
    I have tried search if there anything to configure in VFD - but no luck.

    2. From time to time when reverse direction (M4) is given through UCCNC, spindle starts to rotate in FWD direction. Once stopped and reverse command repeated rotation direction is correct.

    3. Once M3 command is given, spindle is getting up to speed and sometimes even at acceleration process UC300 giving message on screen that motion controller has been disconnected and everything stops. It is not possible to use spindle at the time as UC300 gets disconnected at any time once spindle rotation is activated.
    I tried to play with SFr [Switching freq.] and at 16hz was total nightmare as the UC300 gets disconnected once spindle is started. Currently I left setting at 2hz as this option lets to get spindle up to full speed, but shortly UC300 gets disconnected...

    Current settings for AltiVar320:

    VFD set to SINK mode

    CFG [Macro configuration] - [Gen. Use] (GEn): General use


    tCC [2/3 wire control] - set to 2C


    Ctt [Motor control type] - set to Std


    ACC [Acceleration] - set to 5.0


    dEC [Deceleration] - set to 3.0


    bFr [Standard mot. freq] - set to 50


    nPr [Rated motor power] - set to 0.80


    UnS [Rated motor volt.] - set to 220


    nCr [Rated mot. current] - set to 5.0


    FrS [Rated motor freq.] - set to 400


    nSP [Rated motor speed] - set to 24.00


    tFr [Max frequency] - set to 400


    LSP [Low speed] - set to 0


    HSP [High speed] - set to 400


    SFr [Switching freq.] - set to 2


    FLU [Motor fluxing] - set to FnO [no]


    nrd [Noise reduction] - set to YES


    UiL1 [AI1 min value] - 0v


    UiH1 [AI1 max value] - 4.5v



    I will try do to a factory settings reset and configure once again, but I would appreciate any input on these issues.


    Thank You

    TM

  6. #5
    TM This could be rf noise coming from the spindle or vfd Do you have screen cable between the two. If not just ground the screen at one end.
    ..Clive
    The more you know, The better you know, How little you know

  7. The Following User Says Thank You to Clive S For This Useful Post:


  8. #6
    Clive's comments are very valid, especially as this is a somewhat random problem.

    Couple of points to make, though.

    There are a few parameters in the VFD that control how it drives the spindle. From memory, on my own VFD, these are something like sensorless torque control and V/F. These change the way that the VFD generates its output, and also senses how the spindle is reacting. I'm really not an expert on these and which the best choice is. What I can say is that you seem to be accelerating the spindle quite quickly. This might be OK for your spindle, but perhaps someone else can listen to the video clip and comment?

    Second point is to ask if you can show the parameters that DI1/DI2 are set to. They are probably correct, but it would be good to check. You say that you have set your VFD to 2C mode, which is what I would also do. However, you appear to always enable output 4 to start the spindle, and then enable output 3 for reverse. However, in 2C (2-wire) mode, you should use output 4 for forwards, and output 3 for reverse. Never use 3 and 4 together. This might explain the problem and random starting direction in reverse - depending on whether the BOB sets 3 slightly before or slightly after 4, the VFD could start in forwards or reverse. Make sure that the DI pins are correctly set (one for F, one for R) and configure UCCNC and the UC300 to use one or the other output in conjunction with the analogue signal. Might be the source of at least one of your problems!

  9. The Following User Says Thank You to Neale For This Useful Post:


  10. #7
    Also why would you want to use reverse?
    ..Clive
    The more you know, The better you know, How little you know

  11. #8
    Quote Originally Posted by Neale View Post
    Clive's comments are very valid, especially as this is a somewhat random problem.

    Couple of points to make, though.

    There are a few parameters in the VFD that control how it drives the spindle. From memory, on my own VFD, these are something like sensorless torque control and V/F. These change the way that the VFD generates its output, and also senses how the spindle is reacting. I'm really not an expert on these and which the best choice is. What I can say is that you seem to be accelerating the spindle quite quickly. This might be OK for your spindle, but perhaps someone else can listen to the video clip and comment?

    Second point is to ask if you can show the parameters that DI1/DI2 are set to. They are probably correct, but it would be good to check. You say that you have set your VFD to 2C mode, which is what I would also do. However, you appear to always enable output 4 to start the spindle, and then enable output 3 for reverse. However, in 2C (2-wire) mode, you should use output 4 for forwards, and output 3 for reverse. Never use 3 and 4 together. This might explain the problem and random starting direction in reverse - depending on whether the BOB sets 3 slightly before or slightly after 4, the VFD could start in forwards or reverse. Make sure that the DI pins are correctly set (one for F, one for R) and configure UCCNC and the UC300 to use one or the other output in conjunction with the analogue signal. Might be the source of at least one of your problems!

    Thank you Neale,

    The sensorless parameter in VFD is "Ctt [Motor control type] - uuC (Sensorless vector control)", in last configuration I tried to use "Ctt [Motor control type] - set to Std (Standard motor)". But will make a change and will come back with results :)

    DI1 and DI2 is set to be Forward and reverse inputs, I will double check if there is anything to configure further, once I will be back from work.

    Very good eye Neale on noticing output activation - fantastic :) that explains why in some case spindle rotation dir is unpredictable :). Thing is that I can't have separate pin output for FWD / REV as in UCCNC, if PWM spindle control mode is selected - only PWM control pin and DIR pin are available to set (can't choose FWD / REV pins). Maybe I should go with relay control for FWD / REV functions, in that case, two separate PIN's can be chosen.

    Will tryout and will be back with results :)

    Thanx ! :)

  12. #9
    Quote Originally Posted by Neale View Post
    The installation manual, p48 in the copy I found, shows that there is a switch which will let you do this. See "Sink position using the output power supply for the digital inputs".
    You can also set it to "Source" and use the internal +24V. Whichever you prefer.

  13. #10
    Hi Gents,

    I finally received relay array (8 ch). While I was waiting, reassembled all electronics to proper enclosure:

    Click image for larger version. 

Name:	2016-10-04 22.05.13 (Medium).jpg 
Views:	242 
Size:	133.3 KB 
ID:	19456Click image for larger version. 

Name:	2016-10-08 17.13.59 (Medium).jpg 
Views:	273 
Size:	216.1 KB 
ID:	19457

    While connected only power source, I have wired BOB power inputs (12v) and tried to power on and see if all is good. And my BOB gave some flash and smoke :

    Click image for larger version. 

Name:	2016-10-03 20.35.44 (Medium).jpg 
Views:	244 
Size:	223.1 KB 
ID:	19458Click image for larger version. 

Name:	2016-10-04 14.10.17 (Medium).png 
Views:	238 
Size:	1.37 MB 
ID:	19459

    and here is closeup before this :
    Click image for larger version. 

Name:	HDBB.jpg 
Views:	269 
Size:	337.1 KB 
ID:	19460

    I'm not sure how this happened, but I only see that the bolt I have used, head was too big (even before it was ok..) Anybody see other issue here ? I hope that new BOB will no act same...

    Now I'm waiting for the new BOB to arrive and hopefully get everything going...

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. 2.2KW water cooled spindle and Altivar 12 2.2kW 230V 1ph to 3ph
    By gabi68 in forum Generic Chinese Spindles
    Replies: 11
    Last Post: 14-10-2015, 07:37 PM
  2. Altivar inverter - setting maximum speed
    By JohnHaine in forum Motor Drivers & Controllers
    Replies: 12
    Last Post: 06-01-2015, 09:12 PM
  3. PSU wiring help needed
    By Boyan Silyavski in forum General Electronics
    Replies: 7
    Last Post: 25-06-2014, 11:46 AM
  4. Driver wiring advice needed...
    By Wal in forum General Electronics
    Replies: 17
    Last Post: 09-06-2014, 06:11 PM
  5. Newbie Initial Wiring/Setup
    By Rikk in forum Motor Drivers & Controllers
    Replies: 3
    Last Post: 28-06-2011, 10:19 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •