    Quote Originally Posted by dachopper View Post
    I read in the PDMX manual, if the charge pump signal is disabled, then it will disable the PMDX-126 and all motor drivers. If the drivers are disabled, then they cannot be in fault mode, right?


    Am I missing something regarding the fault loop? or does this sound like it will work?
    Yes, you are missing the fact the Drives will still be OUTPUT a fault signal unless the fault is cleared inside the drives. The PMDX only disables its OWN OUTPUTS it cannot control the Drives OUTPUTS and because you're watching these OUTPUTS with the PMDX INPUTS then the fault signal going to the PMDX will Never be cleared.

    Also, think your misunderstanding the Charge Pump. The function of the Charge pump is to disable the PMDX outputs if the connection to the PC is lost. Shouldn't be used for E-stop or to control drives etc.

    The drives could be reset using the Enable signal but not a good solution IMO because it's relying on software.
    Last edited by JAZZCNC; 16-04-2017 at 09:02 PM.

  2. #12
    I see, I just read this from 882 manual "Reset the drive by repowering it to make it function properly after removing above problems" so, if I have one of the pdmx relays controlling the driver voltage, so it cuts driver voltage on fault, this should accomplish the job, or I can manually cycle 882 drive power to clear ?

    If I'm using the relay, should it be cutting power on the DC side, or AC side of my power supply?

    Nick.

  3. #13
    Click image for larger version. 

Name:	circuit-diagram-1.jpg 
Views:	265 
Size:	384.0 KB 
ID:	21413 try again

  4. #14
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 2 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Quote Originally Posted by dachopper View Post
    I see, I just read this from 882 manual "Reset the drive by repowering it to make it function properly after removing above problems" so, if I have one of the pdmx relays controlling the driver voltage, so it cuts driver voltage on fault, this should accomplish the job, or I can manually cycle 882 drive power to clear ?

    If I'm using the relay, should it be cutting power on the DC side, or AC side of my power supply?

    Nick.
    Always cut the ac side. Cutting the dc side risks blowing up the drives.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  5. #15
    OK - I'm goint to try knock up a more complete schematic, and see what you think

  6. #16
    Click image for larger version. 

Name:	circuit-diagram-2.png 
Views:	184 
Size:	73.7 KB 
ID:	21420again#2

  7. #17
    Don't like this setup because you don't have latching safety circuit. How you have it now soon as you release the E-stop the system becomes active again regardless if the fault is cleared or not.

    Personally, I would run the E-Stop thru Master relay wired so forms latch. This then controls the Killing of power to high powered devices like Drives, Vfd etc. Then informs PMDX E-stop occurred which then does the Rest and turns off its Outputs. The Master Relay can only be Reset by pressing Momentary Button and will only allow the Relay to reset if all faults are clear.
    The E-stop circuit can then be run using 24V giving better noise immunity.

  8. #18
    Ok, But latching or not, the software that is running the machine will go into reset condition the second it receives an E-stop or limit switch touched, until someone physically pushes the reset button in the software, and then clicks on start again in the software. So regardless of weather the E-stop remains latched or not, The PDMX will not activate anything again as the software is in reset active mode? A latching circuit is adding another layer of buttons I have to press to get the machine started again.

    What do you think about the load I was placing on the K2 relay? All i did was look at the rated Watts, or Amps per motor and figure out what that would be at 240 Volts ( 100% conversion) to guess the load at max drain for everything on? It says 10A max in the manual

  9. #19
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 2 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    A key rule is never to trust software!

    What size of machine is this?
    Personally, I'd ensure the e-stop circuit removed all power to anything that moves directly, which if I remember correctly from the PMDX manual, the BOB will kill all outputs as soon as the E-stop signal is lost. However, I'd add an extra relay (the onboard relay is probably not ideally rated for handling PSU start-up surges) controlled directly by the E-stop circuit (adding a reset/latch is reasonably easy - they are a legal requirement for commercial use, but hobbyist use you can do whatever you want as long as it's only you that's going to risk getting injured), which controls power to the drives.
    If the E-stop directly controls the main power relay, then you can use an extra set of contacts in the relay to switch the BOB E-stop input. Unless you're using more than about one KW/KVA of power supply, I'd use a common DIN rail mounted DPDT 10A relay. RS part numbers are 488-2610 for the relay, and 803-376 for the socket to give you an idea of the type - other sources are available.

    Having the main drive power supply active without the BOB active is not a problem, as the BOB/software should prevent any motion from occurring. The big problem arises when you rely on the software to kill things, and the reason you want to kill things is because the software isn't doing what it should, so you really want to make sure the E-stop kills everything, even if the computer/software is doing it's very best to not stop things.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  10. The Following User Says Thank You to m_c For This Useful Post:


  11. #20
    Quote Originally Posted by dachopper View Post
    Ok, But latching or not, the software that is running the machine will go into reset condition the second it receives an E-stop or limit switch touched, until someone physically pushes the reset button in the software, and then clicks on start again in the software. So regardless of weather the E-stop remains latched or not, The PDMX will not activate anything again as the software is in reset active mode? A latching circuit is adding another layer of buttons I have to press to get the machine started again.

    What do you think about the load I was placing on the K2 relay? All i did was look at the rated Watts, or Amps per motor and figure out what that would be at 240 Volts ( 100% conversion) to guess the load at max drain for everything on? It says 10A max in the manual
    Was going to answer this then noticed Moray did the job for me.
    Everyone does it there own way just some do it better than others, it's down to you to decide if think yours is better or not.!

Page 2 of 4 FirstFirst 1234 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. CSMIO-IP/S Driving Relays directly
    By cropwell in forum CS-Lab (CSMIO)
    Replies: 10
    Last Post: 02-01-2017, 01:40 AM
  2. Which PSU and drivers do I need ?
    By eurikain in forum General Electronics
    Replies: 10
    Last Post: 18-08-2015, 11:44 AM
  3. not enough current for relays?
    By Boyan Silyavski in forum General Electronics
    Replies: 17
    Last Post: 17-08-2015, 10:05 AM
  4. FOR SALE: pdmx 107 spindle speed control board
    By dazza in forum Items For Sale
    Replies: 0
    Last Post: 08-05-2014, 02:58 PM
  5. question about relays
    By frankman in forum General Electronics
    Replies: 3
    Last Post: 23-01-2012, 07:47 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •