  1. #11
    If you took manufacturer's info from certain devices, my Chinese servo for instance, you wouldn't even want to plug it in your 13A fused socket:) Steppers are another example. While some people spend their precious time solving complicated equations to do with inductance, back EFM and speed graphs, all I need to know - not being of a brainy disposition - is, can I plug it in with a reasonable margin of safety?

    BTW, do you happen to know the Motor stall current x 1/VFD efficiency of the typical Huanyang/2.2Kw combo? I just can't find it anywhere in the instructions:)

    Edward

  2. #12
    Quote Originally Posted by Edward View Post
    BTW, do you happen to know the Motor stall current x 1/VFD efficiency of the typical Huanyang/2.2Kw combo? I just can't find it anywhere in the instructions:)
    Motor stall current should be on the manufacturer's spec sheet for the motor, VFD efficiency should be on the manufacturer's spec sheet for the VFD but you do to some extent get what you pay for.

    If these are not available then ball park figures can be used from a device of similar specification from a manufacturer that does publish technical data and you'll still be closer to the number you are trying to get than you would be with a clamp meter, spindle running with no/moderate load.

    - Nick
    Last edited by magicniner; 11-09-2017 at 11:05 AM.
    You think that's too expensive? You're not a Model Engineer are you? :D

  3. #13
    Hmmm, unfortunately there are too many variants that affect the actual current draw of a particular device, for instance the forces applied at the cutting end. And often practical experience will tell you more than a myriad of calculations.

    And when I do some heavy cutting, I will observe the current to see where I am in relation to the max current set for the device, it will be interesting to know, that's all.

    I only measured the input current with no load just out of sheer curiosity, nothing else, I am not trying to defy science;)

    Edward
    Last edited by Edward; 11-09-2017 at 12:11 PM.

  4. #14
    Quote Originally Posted by Edward View Post
    Hmmm, unfortunately there are too many variants that affect the actual current draw of a particular device, for instance the forces applied at the cutting end.
    Incorrect
    0/10
    You think that's too expensive? You're not a Model Engineer are you? :D

  5. #15
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    The problem with monitoring the line in current, is it's relation to motor current draw varies depending on the motor speed.

    The motor will only see the full mains voltage when running at the rated speed. Any speed below the rated speed, the voltage applied is proportional to the speed i.e. 50% speed, 50% voltage.
    What this means, if using a 2.2kw spindle rated at 220V with a 220V supply for example, is if you're running at maximum torque, at rated speed you'll be pulling 10A with the spindle ideally seeing 220V, and using 2.2KW. Now if you half the speed, the voltage drops to 110V, but the current remains constant at 10A, and you're only using 1.1KW. The supply voltage is still 220V, and due to the wonders of the switching in VFDs, the VFD will only draw 1.1KW/5A from the supply (that's assuming 100% efficiency - there will be some power loss).

    Now from a spindle monitoring point, the supply current draw is useless, unless you're always going to combine it with the motor speed to get some kind of meaningful figure.


    As for manufacturer's recommendations for supply fusing. They are based on worse case scenarios. Nearly all VFDs (and that includes servo drives, as they are essentially a VFD) have huge instantaneous switch on current surges. When first powered up, they appear as a short on the supply until their internal capacitor bank charges.
    Then due to the switching frequency, you can get very high currents (why noise filters should be fitted), that can cause fuses to fail. Even though the average current will never exceed the rated power, there could be spikes many times the average current, which can be worsened if multiple drives share the same unfiltered supply, due to noise/frequency harmonics. In extreme cases, harmonics can cause wiring to burn out due to overheating, yet not trip any protection system.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  6. #16
    Thank you m_c, for the detailed explanation.

    I am aware of the current spikes on switch on, but if we leave that aside for the moment, I thought that the power line current was also proportional to the current drawn on the motor side, for instance, I thought that if the VFD panel showed an increase of 30% in current, then the inline current would also increase by the same rate. I have not had a chance to observe that. Obviously if that isn't the case, in terms of monitoring the current, the VFD measurement is the one to monitor. Thanks

    Edward

  7. #17
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    It's a common thing that people don't understand the fundamentals of motor current and voltage.
    Current = Torque. Voltage = Speed.
    As motor speed increases, back EMF increases, so you need more voltage to push/drive the required current through the windings.
    As load increases, due to the motor poles dragging further behind the magnetic fields, it takes more current to pull/push the rotor along.

    If you were to run a motor at say 10% rated speed, but still apply rated voltage, you would burn out the windings, as due to the lack of back EMF to limit current, excess current would flow through the windings.
    That's why VFDs reduce the voltage in proportion to commanded speed.

    Then combine that with the glorified switch mode power supply that is a VFD, and the lines can get very blurred, but in nutshell, Power out = Power In.
    So supply current = (motor voltage * motor current) / supply voltage.
    That obviously doesn't allow for any inefficiency, but I'd guess that even cheap VFDs will still have efficiency ratings in the high 90s, as they don't generate any major amount of heat.


    You could use the supply current to calculate spindle power, however without knowing the speed, it's relatively meaningless figure, as max spindle power is proportional to speed, so you end up with a percentage of a proportional power. And that's before you consider any inefficiency in the VFD.
    That's why the VFD motor current figure is far more useful, as it corresponds directly to motor torque, and is measured after any VFD inefficiency, so you can quite easily convert to a percentage of available torque.

    With the KFlop, you could pull that data from the VFD using Modbus, then show it in KMotionCNC.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  8. #18
    Quote Originally Posted by m_c View Post
    Nearly all VFDs (and that includes servo drives, as they are essentially a VFD) have huge instantaneous switch on current surges. When first powered up, they appear as a short on the supply until their internal capacitor bank charges.
    Yet if you follow general industrial practice and leave them powered on, controlling the motor with signals and not VFD input power switching, the ramp-up options give you soft-start options which dramatically reduce surge allowing multiple machines to be run safely on circuits which would not normally allow this.

    I'd appreciate links to technical write-ups of examples of harmonic wiring burnout due to absence of filters as the only machine I run a filter on is my CNC mill where the control system is sensitive and requires a filter and I have 6 other VFD systems in the workshop,
    Regards,
    Nick
    You think that's too expensive? You're not a Model Engineer are you? :D

  9. #19
    Quote Originally Posted by m_c View Post

    With the KFlop, you could pull that data from the VFD using Modbus, then show it in KMotionCNC.
    Thanks m_c. That would be quite handy, as the VFD will be some distance from the computer. However, learning all about Modbus is a little beyond me at this stage;)

    I have my second Kflop now for the router I'm building, it took a little while to be familiarised with it sufficiently to get it fully going, with some simple C code for the probe and so on, but it's been very reliable.

    Edward

  10. #20
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Nick, this link is the first one I've found that explains a bit about the hazards - http://www.ecmweb.com/content/fundamentals-harmonics

    I'm in no way an expert, but the problem with the higher order harmonics, is the higher the frequency passing through a conductor, the more the current travels towards the outside of the conductor. IIRC it's called the skin effect, and is why the insulation is far more likely to fail, despite wiring being adequately sized for the rated voltage/current.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

Page 2 of 3 FirstFirst 123 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Reducing 12v DC to 0.5V DC no more than 1A draw
    By AdCNC in forum General Electronics
    Replies: 18
    Last Post: 31-12-2022, 08:14 PM
  2. New build (my first) can't draw circles.
    By mcyoung in forum Gantry/Router Machines & Building
    Replies: 3
    Last Post: 29-06-2015, 11:22 AM
  3. Understanding how to draw and trim circle's in BobCAD V27
    By peter gillespie in forum BobCAD-CAM
    Replies: 0
    Last Post: 11-06-2015, 03:51 PM
  4. stiffness measurements cnc mk3
    By routercnc in forum Gantry/Router Machines & Building
    Replies: 27
    Last Post: 27-04-2014, 09:00 PM
  5. control signals to draw a circle
    By lakmalp in forum Machine Control Software
    Replies: 3
    Last Post: 16-06-2013, 05:52 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •