    I've just bought a generic 3.0Kw spindle and VFD off Amazon and the first thing I noticed when unpacking it is that there is no CE mark on either the VFD or in the documentation, I though all electronic devices sold within the EU had to carry the CE mark to show compliance with EU safety standards?

    Secondly, and more worrying is that the "Earth" terminal in the VFD is only connected to the backplane of the PCB it's mounted on, there is no protective earth connection to the large exposed aluminium heatsink on the back of the unit, meaning that this could potentially carry 240v if there was a fault in the unit, without tripping the breaker.

    I'm intending to take this up with the seller, but I don't suppose I'll get much of a response. I will also to notify Amazon that they are carrying non compliant and potentially lethal electrical goods and hopefully they will delist them, question is are all Chinese VFD's like this?

  2. #2
    Link.
    Price.
    Brand.

    Without the above it's impossible to know if we should be surprised or not.

    - Nick
    You think that's too expensive? You're not a Model Engineer are you? :D

  3. #3
    Jeff
    I would say yes , its the norm

    Going by the photos in various Chinese 6040 router threads
    earthing is an after thought at best as they work without an earth , don't they !!!

    it would appear the routers normally have the mains earth to the control box fastened to a painted metal surface !!!

    the 220V 3 phase VFD output wired to a chassis mounting plug !!! not a socket
    with no earth wire connected to the water cooled spindle motor
    so I will expect there will be enough leakage current to the spindle motor and the rest of the machine to be felt when touched

    I guess the lack of any earth wiring to the rest of the machine avoids earth loops in the signal wiring to and from the breakout board

    I have a 4 ft LED light that I added an earth to the metal case
    the upside is the 36W LED is brighter than the 2 x 36W florescent light it replaced

    I have also rewired the mini-lathe I have as the push on connectors used was made from brass that was too thin to maintain good contact pressure


    John
    Last edited by john swift; 15-10-2017 at 11:17 PM.

  4. #4
    Jeff's Avatar
    Lives in Filey, United Kingdom. Last Activity: 31-10-2017 Has been a member for 4-5 years. Has a total post count of 19. Received thanks 2 times, giving thanks to others 3 times.
    Here is a link to the unit in question

    https://www.amazon.co.uk/Happybuy-Sp...s=happybuy+3.0

  5. #5
    If you click the sellers name on the line

    "Dispatched from and sold by moretrade."

    You get this -

    https://www.amazon.co.uk/sp?_encodin...b=&vasStoreID=

    Confirming that the items are sold and shipped from Shanghai.

    Unless an item states "Fulfilled by Amazon" Amazon is merely the marketplace and you are dealing with the seller, you have clearly chosen to buy a Chinese product shipped from China and now you want to get it "de-listed" because it isn't CE marked and made to EU electrical safety standards?

    Wire it up with the appropriate safe mounting, earthing and connections and see if it works, if not you have a legitimate gripe.

    - Nick
    You think that's too expensive? You're not a Model Engineer are you? :D

  6. My understanding is that because you are buying directly from China, then it can be imported without a CE mark, but if i were to import it and then sell it from within the EU, i would be breaking the law.
    So if you buy it and put it in a CNC router and sell it, and the person who bought it got electrocuted, then you would most likely be prosecuted if it were found that items on the machine were not safe and had no CE.


    Quote Originally Posted by Jeff View Post
    Here is a link to the unit in question

    https://www.amazon.co.uk/Happybuy-Sp...s=happybuy+3.0
    Last edited by Gary; 16-10-2017 at 12:54 PM.

  7. A long time ago, i was buying stepper drivers from IMS in the USA and they had no CE.
    Parker, complained and we had a letter requesting further information.
    Luckily they were under the low voltage threshold of the LVD and the case was dropped, but if it was not we would most likely have had a large fine and told to stop importing these drivers.

  8. #8
    Jeff's Avatar
    Lives in Filey, United Kingdom. Last Activity: 31-10-2017 Has been a member for 4-5 years. Has a total post count of 19. Received thanks 2 times, giving thanks to others 3 times.
    The item was actually shipped from Germany, so yes it should be CE compliant. I've notified the seller of this and pointed out that if the unit isn't correctly bonded when it's installed it could be potentially fatal. I have every right to expect that electrical products, no matter where they are manufactured at least meet basic safety standards.
    Last edited by Jeff; 16-10-2017 at 05:23 PM.

  9. #9
    Quote Originally Posted by Jeff View Post
    The item was actually shipped from Germany.
    It's just a 3rd party warehousing service used by a Chinese company from Shanghai.
    On the bright side you should only have to send it back to the warehouse for a refund, then you can buy something with a CE mark ;-)

    Quote Originally Posted by Jeff View Post
    I've notified the seller of this and pointed out that if the unit isn't correctly bonded when it's installed it could be potentially fatal.
    But your qualified electrical engineer would have spotted all that and either wired it correctly or condemned it :D
    You think that's too expensive? You're not a Model Engineer are you? :D

  10. It's just a 3rd party warehousing service used by a Chinese company from Shanghai. On the bright side you should only have to send it back to the warehouse for a refund, then you can buy something with a CE mark ;-)
    If it was sent from Germany, it would have been invoiced from Germany, so imported into the EU and resold, so if it is not CE, this is illegal.


    But your qualified electrical engineer would have spotted all that and either wired it correctly or condemned it :D
    Not the point. If it is dangerous it should not be sold regardless of where.

    Also just because it has CE stamped on the device does not make it CE, you should ask for a copy of the certificate and this will give the details of the company who put it through CE and the number that you can check up on.
    Last edited by Gary; 16-10-2017 at 07:03 PM.

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. FOR SALE: Gecko Drive G251 drives + heatsink
    By m_c in forum Items For Sale
    Replies: 4
    Last Post: 18-01-2022, 10:21 PM
  2. CSMIO-M Tool Probe Connection - +24v to earth
    By Noplace in forum CS-Lab (CSMIO)
    Replies: 1
    Last Post: 10-04-2016, 09:17 PM
  3. 3020 / 3040 / generic chinese router accuracy
    By m_c in forum Machine Discussion
    Replies: 2
    Last Post: 24-07-2014, 11:54 PM
  4. Replies: 4
    Last Post: 08-05-2013, 11:31 AM
  5. Adding earth cable to 2.2Kw Chinese Spindle
    By Dwayne Dibbley in forum Generic Chinese Spindles
    Replies: 4
    Last Post: 13-03-2013, 04:04 PM