    Just as the title really, I have been loaned a transwave static converter to try on my Boxford 250.

    I was going to try it as I ve heard that multi motor machines wont work on a static converter.

    Question is will I damage the converter (as its not mine) or worse still damage the lathe if it dosnt work properly?

    Its a 1990's Fanuc Ot controller if that helps.

    Thanks in advance

  2. #2
    what parts of the Boxford 250 need to be run from a 3 phase supply ?

    I would think the Fanuc controller could be run of the single phase supply

    how intelligent is the transwave static converter ?

    if you have to select the capacitors to generate the 3rd phase
    then the phase to phase voltages will change wildly as you switch the various motors on and off
    and risk damaging any motor speed control

    example of simple converter that would not work for your machine
    Click image for larger version. 

Name:	simple 1 to 3 phase converter example.jpg 
Views:	182 
Size:	66.8 KB 
ID:	23850

    John
    Last edited by john swift; 28-02-2018 at 01:05 PM. Reason: add simple converter example

  3. #3
    Ross77's Avatar
    Lives in Devon, United Kingdom. Last Activity: 2 Weeks Ago Has been a member for 9-10 years. Has a total post count of 759. Received thanks 27 times, giving thanks to others 52 times.
    Its the spindle inverter, ac servo drives and the coolant pump. the main Fanuc controller is 110v

    The converter is a Transwave 5.5Kw cant see a model no. but the serial is XHD18487STC

    As it not mine I dont want to open it up to see if its like the example. cheers

  4. #4
    My understanding of static inverters is that they work fine for loads within their rated range, but are not happy with loads that are too small. A 5.5KW inverter is pretty big and will probably have a correspondingly bigger minimum load. Generally I believe that they are happy with running multiple motors BUT the total load must be within the rated range. So, a big lathe might use one for the main drive motor and would be happy with lube/coolant pumps running at the same time but would probably not start aforesaid lube/coolant pumps without the main motor running.

    I would have a look at the Transwave site to see if they give specs there for the permitted range of loads, including minimum load.

  5. #5
    Ross77's Avatar
    Lives in Devon, United Kingdom. Last Activity: 2 Weeks Ago Has been a member for 9-10 years. Has a total post count of 759. Received thanks 27 times, giving thanks to others 52 times.
    Click image for larger version. 

Name:	20180215_190348 (002).jpg 
Views:	169 
Size:	642.8 KB 
ID:	23852

    Looks like 0.75kw min on the plate and the spindle motor is 1.5kw. not sure if the ac servos will pull enough though to move the axis without the spindle running.

  6. #6
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Static converters are no good for anything other than direct motor loads. They rely on the motor spinning, and the corresponding load/backemf and a bank of capacitors to create the generated leg. Without the spinning motor, the generated leg voltage will be all over the place. Even with a motor attached, the generated leg voltage will vary during changing loads. More advanced static converters let you switch capacitors in/out to try and compensate, and some even do it automatically for you.

    However, what you could do, is attach a reasonably sized motor to the static converter, and you have a rotary converter.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  7. #7
    Ross77's Avatar
    Lives in Devon, United Kingdom. Last Activity: 2 Weeks Ago Has been a member for 9-10 years. Has a total post count of 759. Received thanks 27 times, giving thanks to others 52 times.
    However, what you could do, is attach a reasonably sized motor to the static converter, and you have a rotary converter.
    I have just spoken to a very helpful guy at Transwave and he has suggested the same thing, Not ideal but would get me running hopefully.

    More advanced static converters let you switch capacitors in/out to try and compensate, and some even do it automatically for you.
    Yes this one has a switch for the capacitors so I can load up the dummy motor and get it reading right before I power up the lathe, Just have to hope I can get a bigg enough dummy motor to smooth out the voltage.

    Its not ideal but at least i might be able to use the lathe and make sure it will do what I need it to do before spending any more money on a digital converter or a retrofit.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Step/direction to analogue converter
    By Agathon in forum Control Hardware & Systems
    Replies: 3
    Last Post: 10-08-2017, 08:58 AM
  2. Massive Static sparks in dust shoe
    By mturneruk in forum General Discussion
    Replies: 4
    Last Post: 20-01-2016, 12:01 AM
  3. Struggling with USB to RS485 USB-485 Converter
    By kingcreaky in forum Computer Hardware
    Replies: 0
    Last Post: 25-08-2013, 08:04 PM
  4. Replies: 0
    Last Post: 25-01-2012, 09:29 PM
  5. FOR SALE: AXYZ USB to RS-485 optically isolated converter for sale £260 ono
    By RickyThunders in forum Items For Sale
    Replies: 0
    Last Post: 18-07-2011, 11:30 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •