  1. Hello,

    I'm trying to wire the AM882 Fault Alarm ALM on my system,
    the latch reset and e-stop already works.
    The Pilz S5 has 2 inputs, i'was thinking using on input for the limits and one for the am882 alarm, but when one of the 2 input signal is open the relay goes in Fault (red light) and it must be reset by removing the relay supply... 'maybe a problem of setup mode ?

    or 2 I could wire the alarm in series on the estop circuit from the 24v to the inputs of the s5 but adding 3 or 4 inductive proximity sensor in series could be a problem with the maximum 100mA on the AM882 alarm.

    Do you have an idea ?

    Thanks for your help...

    Click image for larger version. 

Name:	electric schema cncpa am882 alarm enable.GIF 
Views:	724 
Size:	88.5 KB 
ID:	24762

  2. Quote Originally Posted by pierantoine View Post
    Hello,

    I'm trying to wire the AM882 Fault Alarm ALM
    I could wire the alarm in series on the estop circuit from the 24v to the inputs of the s5 but adding 3 or 4 inductive proximity sensor in series could be a problem with the maximum 100mA on the AM882 alarm.

    Do you have an idea ?

    Thanks for your help...

    Click image for larger version. 

Name:	electric schema cncpa am882 alarm enable.GIF 
Views:	724 
Size:	88.5 KB 
ID:	24762
    Wiring in series the alarms to the relay input doesn t work...
    Voltage drops from 24 to 8v...
    Last edited by pierantoine; 27-09-2018 at 10:19 PM.

  3. #3

  4. Quote Originally Posted by Nickhofen View Post
    Yes. Thanks.
    But the problem is my 24v after the driver is dropping to 8v when driver is in fault state... And connected to the input of the pilz.

  5. Hello
    I ve still the problem of connecting the am882 alarm with a pilz if you have an idea it can help

    Thanks

  6. #6
    I am sorry to hear that, I hope the help come soon!

  7. #7
    Have a look here;

    http://www.mycncuk.com/threads/6565-...2213#post52213

    Then I found the alarms were wired incorrectly and changed it here;

    http://www.mycncuk.com/threads/6565-...7622#post57622

    This all works well now.
    Last edited by EddyCurrent; 01-05-2019 at 02:57 PM.
    Spelling mistakes are not intentional, I only seem to see them some time after I've posted

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Wiring up the Alarm output on Leadshine AM882
    By Shinobiwan in forum Motor Drivers & Controllers
    Replies: 42
    Last Post: 01-08-2017, 02:07 AM
  2. AM882 Alarm and Enable Signal Question
    By Gotty101 in forum Motor Drivers & Controllers
    Replies: 2
    Last Post: 24-11-2015, 11:07 PM
  3. First CNC build - VFD wiring question
    By Bez in forum Gantry/Router Machines & Building
    Replies: 15
    Last Post: 06-03-2015, 10:44 PM
  4. Pilz Relay info
    By manofgresley in forum General Electronics
    Replies: 5
    Last Post: 08-05-2014, 10:16 PM
  5. AM882 Alarm Circuit
    By Wobblycogs in forum General Electronics
    Replies: 8
    Last Post: 28-03-2014, 06:06 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •