    Hello,

    Thanks for the help, I tried your settings and also other settings, but unfortunately without success.
    I also tried another motor (0.55 KW), unfortunately it shows the same behavior.
    Without load


    With load


    Any ideas?

    Regards Marc
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG-20201222-WA0002.jpg 
Views:	187 
Size:	149.0 KB 
ID:	29373  

  2. #22
    Hooray, a small success!
    I have now got the motor running under load, for this I had to set P72. Unfortunately, the motor now runs very rough in operation. Can someone help me with the torque settings P70, P71 and P72?

    Greetings Marc

  3. #23
    Quote Originally Posted by Spyke View Post
    Hooray, a small success!
    I have now got the motor running under load, for this I had to set P72. Unfortunately, the motor now runs very rough in operation. Can someone help me with the torque settings P70, P71 and P72?

    Greetings Marc
    Something is not right with the fundamental settings. P72 is just for additional torque at low speed. I did not use mine in the end as there was plenty of torque when I did some test drilling.

    How is this wired to the motor ? Delta pattern I assume ? Is this wired correctly at the motor end ?

    How many poles? I assume 2 poles from the rpm ? Is this set correctly ?

    What is the max current set to P76? Maybe this is too low and the P72 is helping you out but it is not the way to solve it.

    Check all connections are tight.
    Building a CNC machine to make a better one since 2010 . . .
    MK1 (1st photo), MK2, MK3, MK4

  4. #24
    It is wired as delta, what do you mean with wired correctly at the motor end? V is V, W is W, U is U.
    Yes its a 2 pole motor. I checked all connections several times and do also a trough check with multimeter.
    Max current is set to 8000.

    I saw in different videos nobody needs torque compensation for starting motor with load.
    It seams that one phase has not enough power and causes the motor stuttering under load. So I think something is wrong with my Vfd.

  5. #25
    Quote Originally Posted by Spyke View Post
    It is wired as delta, what do you mean with wired correctly at the motor end? V is V, W is W, U is U.
    Yes its a 2 pole motor. I checked all connections several times and do also a trough check with multimeter.
    Max current is set to 8000.

    I saw in different videos nobody needs torque compensation for starting motor with load.
    It seams that one phase has not enough power and causes the motor stuttering under load. So I think something is wrong with my Vfd.
    I just meant to check if it is wired delta. If you have an oscilloscope and current clamp you could do some checking but you could be right and the inverter is maybe faulty. Is it new and a recent purchase? See what the seller has to say about it.
    Building a CNC machine to make a better one since 2010 . . .
    MK1 (1st photo), MK2, MK3, MK4

  6. #26
    Quote Originally Posted by routercnc View Post
    I just meant to check if it is wired delta. If you have an oscilloscope and current clamp you could do some checking but you could be right and the inverter is maybe faulty. Is it new and a recent purchase? See what the seller has to say about it.
    It´s a new one, I already contacted the seller, let´s see what he is saying.....Chinese seller.....
    Unfortunately I didn´t have a oscilloscope and current clamp. But the company in the neighborhood of my company have the equipment, I ask them if they can check for me, they are machine builders and familiar with such stuff.

    Attached you can find my settings. Maybe you can find a wrong value.
    Attached Files Attached Files

  7. #27
    Your instructions show P25 as 'not listed' and my instructions show that as the number of poles. 0 = 2 poles, 1 = 4 poles, 2 = 6 poles. Luckily you have set yours to 0 which is 2 poles, although P21 is different and asks for 'rpm for 50 Hz', which I guess is another way to calculate number of poles.

    I can't see anything else wrong, so suspect it is faulty. The Chinese sellers often want some evidence of the fault so your video should help there, plus you have tried 2 different motors. I would wait for them to respond and not dive into asking a company to look at it. If the seller thinks you have opened it up they may not refund you.

    I had a invertor arrive faulty a few years ago (it went bang when I wired it up to the mains - no motor had been fitted) and they wanted to see a photo of the wiring. After showing them the photo they asked me to send it back and they sent another. Good luck.

    Your settings are here, in case others spot something:
    P000 Maximum voltage 220 default V
    P001 Reference frequency 50 default Hz
    P002 Intermediate voltage 110 default V
    P003 Intermediate frequqncy 25 default Hz
    P004 Minimum voltage 0 default V
    P005 Minimum frequency 0 default Hz
    P006 Maximum operating 50 65 Hz
    P007 Minimum operating 0 default Hz
    P008 Hide password 0 default -
    P009 Input password 0 default -
    P010 Working frequency source 1 default -
    P011 Start/stop control source 0 default -
    P012 Stopping Modes 1 default -
    P013 Braking time 0,5 default S
    P014 Braking voltage 20 default V
    P015 not listed 2 not listed -
    P016 not listed 1 not listed -
    P017 Machine number 1 default -
    P018 Operating arrival 50 default Hz
    P019 not listed 50 not listed -
    P020
    Over temperature
    protection selection 80 default -
    P021 Revolution for 50Hz 2730 2800 -
    P022 Carrier setting 10 default -
    P023 Frequenzy adjusting step size 5 default 0.1Hz
    P024 Overload protection buffer time 3 default S
    P025 not listed 0 not listed -
    P026 Working frequency 50 default Hz
    P027 Section speed 1 setting 45 default Hz
    P028 Section speed 2 setting 40 default Hz
    P029 Section speed 3 setting 35 default Hz
    P030 Section speed 4 setting 30 default Hz
    P031 Section speed 5 setting 25 default Hz
    P032 Section speed 6 setting 20 default Hz
    P033 Section speed 7 setting 15 default Hz
    P034 Main rising velocity 8 25 Hz/S
    P035 1st rising velocity 25 default Hz/S
    P036 2nd rising velocity 25 default Hz/S
    P037 3rd rising velocity 25 default Hz/S
    P038 4th rising velocity 25 default Hz/S
    P039 5th rising velocity 25 default Hz/S
    P040 6th rising velocity 25 default Hz/S
    P041 7th rising velocity 25 default Hz/S
    P042 Main descent velocity 20 default Hz/S
    P043 1st descent velocity 25 default Hz/S
    P044 2nd descent velocity 25 default Hz/S
    P045 3rd descent velocity 25 default Hz/S
    P046 4th descent velocity 25 default Hz/S
    P047 5th descent velocity 25 default Hz/S
    P048 6th descent velocity 25 default Hz/S
    P049 7th descent velocity 25 default Hz/S
    P050 Multi function input 1 (X1) 13 default -
    P051 Multi function input 2 14 default -
    P052 Multi function input 3 15 default -
    P053 Multi function input 4 5 default -
    P054 Multi function input 5 6 default -
    P055 Multi function input 6 9 default -
    P056 not listed 0 not listed -
    P057 not listed 0 not listed -
    P058 Multi function input 1 (SP1) 0 default -
    P059 not listed 0 not listed -
    P060 Multi function input 2 0 default -
    P061 not listed 0 default -
    P062 Display options 1 0
    (not changed by me) -
    P063 not listed 0 not listed -
    P064 not listed 0 not listed -
    P065 Power on options 0 default -
    P066 Input stabilisation time 60 default mS
    P067 Voltage coefficient 28500 default -
    P068 Under voltage setting 60 default V
    P069 Overvoltage setting 400 default V
    P070 Torque compensation options 0 default -
    P071 Torque compensation voltage 10 default V
    P072 Torque compensation setting 55 0 -
    P073 Maximum external analog 31440 default -
    P074 Minimum external analog 2096 default -
    P075 Zero current compensation value 1130 default -
    P076 Current coefficient 9500 default -
    P077 Parameter reset 0 default -
    P078 Main current overload 8000 3000 mA
    P079 First current overload 3000 default mA
    P080 Second current overload 3000 default mA
    P081 Third current overload 3000 default mA
    P082 Fourth current overload 3000 default mA
    P083 Fifth current overload 3000 default mA
    P084 Sixth current overload 3000 default mA
    P085 Seventh current overload 3000 default mA
    P086 Jog forward frequency 20 default Hz
    P087 Jog reverse frequency 20 default Hz
    P088 Jog rising velocity 25 default 50
    (not changed by me) Hz/S
    P089 Jog descent velocity 25 default 50
    (not changed by me) Hz/S
    P090 Jog stopping modes 2 default 1
    (not changed by me) -
    P091 Jog braking time 0,1 default S
    P092 Phase options (AT2 only) 0 default (only AT2) -
    P093 not listed 16384 not listed -
    P094 not listed 49152 not listed -
    P095 not listed 0 not listed -
    P096 not listed 1 not listed -
    P097 not listed 0 not listed -
    P098
    The frequency of
    closing the U-Phase (AT2) 0 default (only AT2) Hz
    P099 not listed 0 not listed -
    P100 not listed 30000 not listed -
    P101 not listed 0 not listed -
    P102 not listed 32 not listed -
    P103 not listed 280 not listed -
    P104 not listed 260 not listed -
    P105 not listed 0 not listed -
    P106 not listed 0 not listed -
    P107 not listed 13001 not listed -
    P108 not listed 0 not listed -
    P109 not listed 0 not listed -
    P110 not listed 500 not listed -
    P111 not listed 0 not listed -
    P112 not listed 0 not listed -
    P113 not listed 0 not listed -
    P114 not listed 0 not listed -
    P115 not listed 0 not listed -
    P116 not listed 0 not listed -
    P117 not listed 0 not listed -
    P118 not listed 0 not listed -
    P119 not listed 0 not listed -
    P120 not listed 0 not listed -
    P121 not listed 0 not listed -
    P122 not listed 0 not listed -
    P123 not listed 30000 not listed -
    P124 not listed 0 not listed -
    P125 not listed 0 not listed -
    P126 not listed 0 not listed -
    P127 Remaining hours 65535 default H
    Building a CNC machine to make a better one since 2010 . . .
    MK1 (1st photo), MK2, MK3, MK4

  8. #28
    I ordered an other one on Amazon, because I plan also to rebuilt my drill press.

  9. #29
    My VFD is faulty, today my second on from Amazon arrived and everything works well.
    I'm in contact with the seller of the first one, he is very cooperative and will send replacement.

    Thanks' for your help!

    Regards
    Marc

  10. #30
    i am so satisfacted.my english is poor, sorry :). thx for approving my user greetings wally

Page 3 of 5 FirstFirst 12345 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. HELP! Colchester CNC 350 + Fanuc Series O-T Parameters - Diagnostics
    By Constantin in forum Lathes, Lathe Rebuilding & Conversions
    Replies: 1
    Last Post: 26-08-2019, 05:38 AM
  2. Replies: 14
    Last Post: 19-10-2017, 02:34 PM
  3. 3020 / 3040 / generic chinese router accuracy
    By m_c in forum Machine Discussion
    Replies: 2
    Last Post: 24-07-2014, 11:54 PM
  4. Optimize parameters for mills with tips
    By hoezap in forum Tool & Tooling Technology
    Replies: 0
    Last Post: 15-06-2013, 01:18 PM
  5. G4 Dwell parameters
    By mmcp42 in forum Programmers Corner
    Replies: 10
    Last Post: 31-12-2010, 04:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •