Page 1 of 3 123 LastLast
  1. #1
    Well Doddy said I would be back - and here I am.

    Some of my toolpaths take a day or so to run and I want to turn a compressor on for certain operations to blow away the swarf, hopefully using M8/M9. To slightly complicate things the compressor in the workshop is currently wired with a 2 way switch so it can be turned on and off from either upstairs or downstairs and I need to keep this fuctionality.

    Can anyone suggest a wiring circuit that would enable my AXBB_E controller to seamlessly turn the compressor on and off?

    Hope this makes sense and looking forward to suggestions.

    Carl

  2. #2
    Bypass the 2-way Upstairs/Downstairs switches entirely by using a relay, triggered from AXBB_E. That just means that AXBB can override the manual switches to power-up the compressor - and have the switches turned off in this mode. You could use another output from the AXBB and a M9999 macro to automatically isolate the manual switches when UCCNC starts up, if that tickles your fancy. All do-able, just need to understand the exact control logic that you're looking to implement.

  3. #3
    Thanks Doddy - I did think this would be right up your street.

    Regarding the logic I only need the compressor on certain parts so whatever I do I would like it to work in a way so I don't have to re-programme existing parts so don't think having UCCNC take control on startup would be the right way to go. Is there a relay available that when an M8 call is made the manual switches are isolated and power supplied to the compressor. If it makes any dfferece when an M8 call is made there will be at least 30 minutes before the compressor is turned off

    EDIT: I have found this OMRON MK2P-S relay left over after my retro-fit. With my limited electrical knowledge I think it fits the bill? Click image for larger version. 

Name:	omron.jpg 
Views:	146 
Size:	153.1 KB 
ID:	28887
    Last edited by ngwagwa; 21-09-2020 at 02:28 PM.

  4. #4
    Something like

    Click image for larger version. 

Name:	Screenshot 2020-09-21 at 19.21.03.png 
Views:	148 
Size:	76.2 KB 
ID:	28888

    All depends on your use-case. In this example UCCNC simply bypasses the manual switches to force the compressor on. Set the M8 command pin/port on setup/spindle page.

    You would still be able to turn on the compressor with the existing switches, but not turn off the compressor with the switches if enabled by the AXBB.

    That relay?, if it's the right coil voltage and current to suit the AXBB?

    EDIT: You could glam up the circuit but there's a certain KISS approach to the above.

  5. #5
    I had a play and came up with this Click image for larger version. 

Name:	compresor with relay.JPG 
Views:	147 
Size:	30.9 KB 
ID:	28889
    It does what your diagram does but also isolates the live from the 2 way switches when UCCNC has control.

  6. #6
    The old way with household wiring was to use an "intermediate" switch . Could you not wire a relay to provide similar
    http://www.lightwiring.co.uk/wp-cont...ng-diagram.jpg

  7. #7
    Quote Originally Posted by John11668 View Post
    The old way with household wiring was to use an "intermediate" switch . Could you not wire a relay to provide similar
    http://www.lightwiring.co.uk/wp-cont...ng-diagram.jpg
    That would give me a circuit like this (I think) you will have to forgive me I have some sort of mental block when it come to even the simplest wiring.
    Click image for larger version. 

Name:	compresor intermediate relay.JPG 
Views:	126 
Size:	36.5 KB 
ID:	28890

    An intermediate would work but I would prefer it so that when UCCNC is calling to air it can't be overridden.

  8. #8
    Couple of caveats -

    You don't 'need' to isolate the switch circuit. But doing so does no harm.

    You'll be back - I reckon within a couple of weeks - to complain that, whilst under UCCNC control someone switched the compressor on accidentally, and after UCCNC has quit that the compressor has been left operating. That's a more complicated problem!

  9. #9
    Quote Originally Posted by Doddy View Post
    Couple of caveats -

    You'll be back - I reckon within a couple of weeks - to complain that, whilst under UCCNC control someone switched the compressor on accidentally, and after UCCNC has quit that the compressor has been left operating. That's a more complicated problem!
    You could use a C/O contact on the relay to gate the building wiring into a contact that, if M8 is active, and the building wiring "live" (i.e. it would hold the compressor on after M9) that it illuminates a lamp or sounds an alarm, or something. But that would require that you isolate that circuit from the compressor under M8 control.

  10. #10
    Quote Originally Posted by Doddy View Post
    Couple of caveats -

    You don't 'need' to isolate the switch circuit. But doing so does no harm.

    You'll be back - I reckon within a couple of weeks - to complain that, whilst under UCCNC control someone switched the compressor on accidentally, and after UCCNC has quit that the compressor has been left operating. That's a more complicated problem!
    Doddy - is my circuit in post #5 feasible? If so UCCNC has control so the manual switches have no effect.

    Regarding the compressor being left on I already have a signal lamp which comes on when the compressor is powered - this was put in before the 2 way switches as the compressor was often left running! The lamp is visible from our in workshop CCTV camera and we have a networked smart switch so the compressor can be turned off remotely

Page 1 of 3 123 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. BUILD LOG: Quite an Unusual one
    By Boyan Silyavski in forum DIY Router Build Logs
    Replies: 205
    Last Post: 18-04-2023, 06:04 PM
  2. An unusual problem
    By racerbear02 in forum Machine Discussion
    Replies: 5
    Last Post: 10-01-2016, 11:45 AM
  3. Unusual Knife Block
    By Christian Knuell in forum Woodworking Project Showcase
    Replies: 1
    Last Post: 10-09-2014, 11:28 AM
  4. Which air compressor?
    By newtoid1986 in forum General Discussion
    Replies: 7
    Last Post: 12-12-2011, 04:07 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •