    I have been looking at your diagram for the limit switches trying to understand what you are trying to achieve. All the NPN/PNP proximity switches I have looked at require 0V and a positive DC supply as inputs to power the sensor, and give a switched output. I do not think the way you have shown them will work. Do you have a link to a datasheet for the sensors ?

    Can I also make a suggestion to you - don't mark the AC inputs to power supplies with a "+" and "-" which implies DC. It would be very easy to connect all the "-" terminals together which would not be a good move.

    Graeme

  2. #562
    Graeme, the way I was trying to wire it up was that they were all linked and as they are NC that any sensing will drop out the power to the circuit (and at the same time light a lamp to indicate that a limit has been hit, may put in a buzzer too) I think I've got my head in manual switch mode and not proxy mode. Was all done in a rush, no excuse I know....

    Again I was being lazy with the labeling and jyst copying and pasting....I'll put L & N on tomorrow.
    Last edited by njhussey; 30-03-2015 at 10:32 PM.
    Neil...

    Build log...here

  3. #563
    Neil bit hard to read these schematics but looks to me on the power and Safety diagram you got something wrong.?
    The Live is going thru the door contactor then into the 24Vdc contactor but you'll have no 24Vdc because 24vdc PSU is picking live up from other side of 24dc contactor which will never turn on.!

    Need pick Live up for 24Vdc PSU before going into 24dc Contactor mate.

    Next Limits. Other than what Graeme mentioned is the way you have wired Input from IP-M.? The inputs don't provide Voltage Ref you provide it one. So send 24vdc thru the Relay NO Contact to Input (+) and take Input (-) to 0Vdc.
    Last edited by JAZZCNC; 31-03-2015 at 12:43 AM.

  4. #564
    Quote Originally Posted by JAZZCNC View Post
    Neil bit hard to read these schematics but looks to me on the power and Safety diagram you got something wrong.?
    The Live is going thru the door contactor then into the 24Vdc contactor but you'll have no 24Vdc because 24vdc PSU is picking live up from other side of 24dc contactor which will never turn on.!
    It will certainly be safe then!!!!

    Need pick Live up for 24Vdc PSU before going into 24dc Contactor mate.
    Done...

    Next Limits. Other than what Graeme mentioned is the way you have wired Input from IP-M.? The inputs don't provide Voltage Ref you provide it one. So send 24vdc thru the Relay NO Contact to Input (+) and take Input (-) to 0Vdc.
    Cheers Dean I'm on this....wasn't quote sure how the IP-M worked with regards to the inputs, getting it clearer now.
    Neil...

    Build log...here

  5. #565
    OK, diagrams re-done...please check them as I can't see the wood for the trees!

    Click image for larger version. 

Name:	Limit switch wiring diagram.jpg 
Views:	300 
Size:	252.0 KB 
ID:	15033

    On the drive enable I take it that just closing the circuit is enough, no voltage needs to be applied?

    Click image for larger version. 

Name:	Power and safety wiring diagram.jpg 
Views:	393 
Size:	148.6 KB 
ID:	15031

    I'll start numbering the wires once it's good to go...
    Last edited by njhussey; 31-03-2015 at 12:13 PM.
    Neil...

    Build log...here

  6. #566
    I can see a couple off issues with your limit switches (I think). Firstly without your Override switch being pressed, the state of the limit switches is not passed on to the CSMIO due to the relay contacts being open. Also as you are using NC sensors and have all six in parallel the only way for the CSMIO to see a change is if ALL sensors are activated.
    I do not know what the enable does to the motor drivers, but as I see it pressing the override switch will either allow the motors to work or stop them. Nothing else can affect the enable. I think you need to look at how you are using the override switch.
    I think it might become a little clearer if you view the sensors as switches like in this image

    I am not sure if you can achieve what you are trying with NC sensors.
    Graeme
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	pnp-sensor.jpg 
Views:	811 
Size:	4.1 KB 
ID:	15034  

  7. #567
    Graeme, sorry, I've deleted one too many lines, there should be a line to the A1 of the contactor giving it power from the common line of the sensor. The way I am seeing it is that the contactor is NO until 24V is put on to the coil then it closes the contacts hence making the circuit, the enable is then open which means it's unconnected and enabled and allowing the drive to send pulses to the stepper. Any sensor being activated will break the circuit and the limit switch overide will need to be pressed to put power back on the contactor so I can back the machine off the sensor. Pressing the overide switch will sound the warning buzzer.

    Click image for larger version. 

Name:	Limit switch wiring diagram.jpg 
Views:	270 
Size:	258.7 KB 
ID:	15035
    Neil...

    Build log...here

  8. #568
    give me a spanner any day.....I bloody hate electronics!!!

    OK rant over.....just been down stairs and connected the 24V DC PSU up to the limit switches (2 only) I wired them so that the neutrals all went to a common din rail terminal, the signal from the first went to the +ve of the second and I measured from the neutral to the signal of the second with my multimeter. It lit both lights of the sensors and when any sensor was activated the 24V DC went to zero which was a result....far better playing with things than thinking about them on paper or screen!!!

    New Wiring Diagram...
    Click image for larger version. 

Name:	Limit switch wiring diagram.jpg 
Views:	301 
Size:	247.3 KB 
ID:	15041

    Click image for larger version. 

Name:	Limits_test_1.jpg 
Views:	278 
Size:	386.8 KB 
ID:	15037

    Click image for larger version. 

Name:	Limits_test_2.jpg 
Views:	276 
Size:	377.7 KB 
ID:	15038

    Click image for larger version. 

Name:	Limits_test_3.jpg 
Views:	302 
Size:	394.8 KB 
ID:	15039

    Click image for larger version. 

Name:	Limits_test_4.jpg 
Views:	282 
Size:	372.1 KB 
ID:	15040
    Last edited by njhussey; 31-03-2015 at 03:49 PM.
    Neil...

    Build log...here

  9. #569
    Quote Originally Posted by njhussey View Post
    give me a spanner any day.....I bloody hate electronics!!!

    OK rant over.....just been down stairs and connected the 24V DC PSU up to the limit switches (2 only) I wired them so that the neutrals all went to a common din rail terminal, the signal from the first went to the +ve of the second and I measured from the neutral to the signal of the second with my multimeter. It lit both lights of the sensors and when any sensor was activated the 24V DC went to zero which was a result....far better playing with things than thinking about them on paper or screen!!!
    That looks better but be aware that you are wiring switches in series which contery to popular belief does work with Prox switches but just be aware that reaction time drops the more you have but it's not a problem with only 4 switches.

  10. #570
    OK I see what you are trying to do. Probably not what the manufacturer intended, but as all you are really interested in is the sensors switching off it should work fine.
    Still a little unclear in my mind as to why you are taking the output from the sensors through the relay to you CSMIO. When the same signal is used to turn the relay on/off. Why not take the sensor output directly to the CSMIO ? could you please explain.

Page 57 of 82 FirstFirst ... 747555657585967 ... LastLast

Thread Information

Users Browsing this Thread

There are currently 4 users browsing this thread. (0 members and 4 guests)

Similar Threads

  1. Does anyone want to build me a cnc router?
    By totally useless in forum Open Source Designs & Plans
    Replies: 25
    Last Post: 05-05-2014, 12:44 AM
  2. My new, and first build....comments greatfully received
    By berk in forum Gantry/Router Machines & Building
    Replies: 7
    Last Post: 12-01-2014, 03:15 PM
  3. BUILD LOG: CNC Router New Build
    By PilotTom in forum DIY Router Build Logs
    Replies: 12
    Last Post: 25-05-2013, 03:49 PM
  4. BUILD LOG: A3 Router Build
    By GTJim in forum DIY Router Build Logs
    Replies: 6
    Last Post: 17-02-2012, 12:53 PM
  5. CNC construction TUNISIA give your comments
    By ali hedi in forum Gantry/Router Machines & Building
    Replies: 5
    Last Post: 06-07-2011, 11:58 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •