  1. #1
    Hi,
    Does anyone have any experience running a 10hp cnc router (plus 10hp vac pump) using a 3 phase converter?
    If so, can you suggest a good UK manufacturer of rotary converters.
    Thanks,
    Tom

  2. #2
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    I don't have experience of running motors that big, but you're looking at 30A current at 240v under full load for each motor, and start up current is going to be far higher, which you'll really struggle with using any normal single phase supply.

  3. #3
    Why not use a VFD? Obviously expensive for that size, but the starting current is much much less as you can set the acceleration to a long time. Still as m_c said 10hp/7.46kW is a lot for a normal supply, but will you actually be running the motors at full load?

  4. #4
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    The other issue is the motors might not be able to run on 240V, so you'd also have to factor in a step-up transformer. Even if the motors are capable of running on 240V, then you'll still need to change the control gear.

    In short, it's going to be expensive.

  5. #5
    Quote Originally Posted by m_c View Post
    The other issue is the motors might not be able to run on 240V, so you'd also have to factor in a step-up transformer.
    If the coils can't be swapped round in the motor then if it is acceptable to have a fraction of the rated power then it can still be run on 240V.

  6. #6
    Quote Originally Posted by Jonathan View Post
    If the coils can't be swapped round in the motor then if it is acceptable to have a fraction of the rated power then it can still be run on 240V.
    True but you would want to know how the current increases as the voltage drops and the net effect on the temperature, so not a safe assumption.

    I use a much smaller TransWave which I have been very happy with the tech support for, so would recommend you talk to them for a baseline of what would solve your requirement.

  7. #7
    Quote Originally Posted by Jon S View Post
    True but you would want to know how the current increases as the voltage drops and the net effect on the temperature, so not a safe assumption.
    Yes, hence de-rating the power. Would need to work it out properly first of course...

  8. #8
    I am somewhat baffled about where this idea of running the motors at a lower voltage has come from, my rotary converter on 240v single phase gives 415v on 3 phases.

  9. #9
    Quote Originally Posted by Jon S View Post
    I am somewhat baffled about where this idea of running the motors at a lower voltage has come from
    A VFD run from a 240V supply just rectifies the input, so unless it includes a voltage doubler on the input (don't know if that's something that's available, wouldn't be surprised) it cannot run the motor on 415v.

    This article explains about the various ways:
    http://reviews.ebay.co.uk/3-THREE-PH...00000001476333

  10. #10
    Well clearly from the ebay article you cite Rotary phase converters are a thing of the past.

    Edit - Sarcasm is so easy :-) The chap is clearly considering his options and they are problematic in any direction, I am sure he is aware of that and not planning to install in his attic !

    Cheers,

    Jon
    Last edited by Jon S; 07-12-2011 at 04:20 PM.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. FOR SALE: Leinen Lathe - L4Z - 3 Phase
    By HiltonSteve in forum Items For Sale
    Replies: 0
    Last Post: 24-12-2013, 11:28 AM
  2. FOR SALE: Inverters 3.7Kw 3 phase
    By Ralph in forum Items For Sale
    Replies: 2
    Last Post: 28-07-2013, 03:03 PM
  3. convert 3 phase to single phase?
    By D-man in forum General Electronics
    Replies: 10
    Last Post: 06-04-2013, 12:16 AM
  4. Wiring 3 phase
    By Robin Hewitt in forum General Electronics
    Replies: 16
    Last Post: 10-07-2012, 11:07 PM
  5. Panasonic 3 phase driver running on 1 phase?
    By gavztheouch in forum Motor Drivers & Controllers
    Replies: 2
    Last Post: 10-05-2012, 11:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •