    Quote Originally Posted by crossleymarko View Post
    are all the wire colours on the tororial universal...?
    Try this one:
    http://www.arceurotrade.co.uk/projects/PSU/index.html
    (I notice that diagram has fuses on the secondary side, however I did not include them since each stepper driver already has an internal fuse to protect against over-current. Also any 'nuisance' blowing of that fuse could damage the stepper drivers.)


    The colours are not universal, however there is always a clear diagram on the transformer which labels which colour is which.

  2. #12
    Quote Originally Posted by Jonathan View Post
    Also any 'nuisance' blowing of that fuse could damage the stepper drivers.
    No the fuse is on the supply input. Stepper drives are damaged when the motor supply leads are interfered with.
    John S -

  3. #13
    Quote Originally Posted by John S View Post
    No the fuse is on the supply input. Stepper drives are damaged when the motor supply leads are interfered with.
    It's on both sides in the diagram on Arc Euro. Stepper drivers can be damaged if the power wires are suddenly unplugged for similar reasons to doing the same to the motor wires. It's less likely but still possible since interrupting the current causes a high dI/dt which will cause a voltage spike.

  4. #14
    ok so in stead of a couple caps.. hows this one...

    http://www.rapidonline.com/Electroni...acitor-11-3234

  5. #15
    Quote Originally Posted by crossleymarko View Post
    ok so in stead of a couple caps.. hows this one...

    http://www.rapidonline.com/Electroni...acitor-11-3234
    You would still ideally want two of those. No reason to spend £10 on a high quality capacitor when three £0.82 capacitors in parallel will do the job better.

  6. #16
    Quote Originally Posted by Jonathan View Post
    It's on both sides in the diagram on Arc Euro. Stepper drivers can be damaged if the power wires are suddenly unplugged for similar reasons to doing the same to the motor wires. It's less likely but still possible since interrupting the current causes a high dI/dt which will cause a voltage spike.

    So what happens when the onboard fuse goes or does that behave differently ?
    John S -

  7. #17
    overkill is my theory for future upgrades.. same with the transformer. what would you recomend for overkill..
    also i read it as your stepper is rated at x volts. how is the homebrew psu regulated.. to said volts..

  8. #18
    Never rely on colour codes being universal, not even from the same maker, just something I found out.......

    Colours for the trafo linked to by Jonathan are in the PDF:

    http://www.rapidonline.com/pdf/88-3781.pdf

    Grey and Violet are joined, Blue is Neutral, Brown is live on primary.

    Orange and Black joined are 0V

    Yellow and Red joined are +V on secondary

    Steppers are current driven rather than voltage, the drives take care of the current regulation just need a stiff enough power supply and will drive enough volts through to maintain current.

    Cheers
    Adam
    Last edited by Musht; 05-04-2012 at 01:01 PM.

  9. #19
    so orange and black is -v on the secondry... think i get it. how you worked that out i have no idea.. as grey is 115v and violet is 0 volts.

    also on the description ie. 500va 0-35 0-35.

    does this mean its 70v output.
    Last edited by crossleymarko; 05-04-2012 at 10:18 PM.

  10. #20
    Quote Originally Posted by crossleymarko View Post
    how you worked that out i have no idea.. as grey is 115v and violet is 0 volts.
    The position of the black dot on the diagram shows the relative polarity of the windings, so if a primary wire with a dot is connected to one without, and the other two are connected to the mains that's correct for 230V. If the dotted wires are connected together, then to the mains and similarly for the wires without the dot then the primary windings are in parallel and in phase, so 115V is required - i.e. ideal for the countries with 115V mains (e.g. USA). Any other connection is not permitted since it will involve connecting the windings 180° out of phase, so they'll approximately cancel and you'll get nothing.

    Quote Originally Posted by crossleymarko View Post
    also on the description ie. 500va 0-35 0-35.

    does this mean its 70v output.
    If you put the two secondary windings in series then yes you would get 70V, however we want them in parallel to get 35V at twice the current as if they were in series. Most transformers are wound with at least two secondaries to give you this option.

Page 2 of 3 FirstFirst 123 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. eBay TB6560 Stepper Motor Driver Boards
    By Mad Professor in forum Motor Drivers & Controllers
    Replies: 129
    Last Post: 22-08-2018, 05:32 PM
  2. Ebay CNC motor kits? Any good?
    By gr8fun in forum Gantry/Router Machines & Building
    Replies: 7
    Last Post: 01-12-2012, 10:58 PM
  3. eBay TB6560 Stepper Motor Driver Boards
    By irving2008 in forum Motor Drivers & Controllers
    Replies: 13
    Last Post: 07-04-2010, 04:48 PM
  4. manual for eBay TB6560 Stepper Motor Driver Boards?
    By Dan Brown in forum Motor Drivers & Controllers
    Replies: 5
    Last Post: 06-01-2010, 10:37 PM
  5. CNC Kits
    By itbookham in forum Milling Machines, Builds & Conversions
    Replies: 5
    Last Post: 10-11-2009, 02:56 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •