Thread: RCD tripping

  1. #1
    Keep tripping the rcd in the workshop. I have had a spark check the wires for earth leak and all seems ok. Anyone had problems with a VFD causing this sort of problem? I am reluctant to go to far with replacing wiring as if all works out I will be building a new workshop soon.

    Bruce
    The more I know, I know, I know the less. (John Owen)

  2. #2
    A vfd could be causing the problem but then again so could a pc or anything with power supply in it.
    This could also be because the rcd is faulty as well and tripping below its rated current. Did the spark check the rcd with an rcd tester?

  3. #3
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 1 Hour Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Are you switching both neutral and live to the VFD?
    If you are, change it so you're only switching the live. I've had this problem in the past, and now whenever wiring up a VFD, I just switch the live.

    Some details can be found at HowTo: How to Use Inverter Drives with RDC Earth Leakage Protected Supplies

  4. #4
    Now that Im not on my phone and I can see the site properly,when does the rcd trip? Is it at power up, starting the spindle or after it has been running for a while? Does the rcd trip at any other time? Is this the main rcd on the distribution board or do you have a separate one for the vfd circuit? This could also be an accumulation of leakage from various devices in the workshop and the vfd is just enough to add to it to trip the rcd.

  5. #5
    Guys thanks for all the help. Been ill and so not been up to doing much. I did though find the problem. One of the wires to the spindle had broken the joint so was flapping about and presumably touching to earth. Sorted. The workshop/garage is about to be replaced and extended a further 2.2 mtrs and will be a bit higher. Then the electrics will be installed properly without trailing leads connecting everything.

    Bruce
    The more I know, I know, I know the less. (John Owen)

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. VFD Tripping an RCD
    By Washout in forum Spindles & Drive Motors
    Replies: 13
    Last Post: 04-09-2017, 02:07 PM
  2. VFD (?) tripping RCD
    By Jonathan in forum Spindles & Drive Motors
    Replies: 22
    Last Post: 03-12-2011, 08:19 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •