    Quote Originally Posted by irving2008 View Post
    Yes, it's generally true and often much less in practice. But you do need enough bulk smoothing capacitance to cope with the occasional peak demand.
    With my maximum of 24A (6 motors at 4A) should I go with 500VA or 630VA and what capacitance do I need for smoothing?

    On the webpage of the toroid manufacturer the calculations are slightly different, and I'm a bit confused, probably I should ask them.

    Full wave bridge (FWB) With capacitor:
    VAC = 0.8 x ( VDC +2 )
    IAC = 1.8 x IDC
    WATTS = VDC x IDC (output)
    VA = 1.4 x ( WATTS + 2 IDC* )

  2. Quote Originally Posted by paulus.v View Post
    With my maximum of 24A (6 motors at 4A) should I go with 500VA or 630VA and what capacitance do I need for smoothing?

    On the webpage of the toroid manufacturer the calculations are slightly different, and I'm a bit confused, probably I should ask them.

    Full wave bridge (FWB) With capacitor:
    VAC = 0.8 x ( VDC +2 )
    IAC = 1.8 x IDC
    WATTS = VDC x IDC (output)
    VA = 1.4 x ( WATTS + 2 IDC* )
    Those calcs are for steady state load and make assumptions about power factor etc. to limit core heating and losses. If you go that route you'll end up with a massively overspec'd, physically large and overpriced transformer.

    Steppers are nothing like that, the duty cycle is nothing like steady state. I don't know why you have 6 motors but I'd be surprised if you need more than 60% of the total load and most of the peakiness is handled by the capacitors.

    So use:
    VAC = (VDC + 1.5)*0.7
    IAC = IDC
    VA = IAC * VAC, then chose next largest

    for 2 parallel secondary windings each is rated at IAC/2

    The 1.5 is voltage drop across rectifier, can be 1, 1.5 or 2 depending on product.

    So 24A @ 60% = 15A approx. = IAC (or 2 windings @ 7.5A each)
    VAC = (42+1.5)*0.7=30V
    VA = 30*15=450 so use 500 or 625VA

  3. #13
    Thank you a lot for your help.

    I willl go with 500VA.

    Can you recommend the capacitors specs that I will be needing?

    Quote Originally Posted by irving2008 View Post
    Steppers are nothing like that, the duty cycle is nothing like steady state. I don't know why you have 6 motors but I'd be surprised if you need more than 60% of the total load and most of the peakiness is handled by the capacitors.
    I intend to build a lightweight 2 axis head for 3D foam milling and a rotary axis for wood.

  4. #14
    Can anyone recommend the needed capacitance for smoothing a 30V 500VA AC --> 42V 16.5A DC toroid?

    If someone could point them on this site I would be very grateful. I found this ones but not sure if I need them to be DC.

    Thanks

Page 2 of 2 FirstFirst 12

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Toroidal Transformer
    By Carlb1058 in forum General Electronics
    Replies: 7
    Last Post: 17-08-2013, 06:54 AM
  2. Stepper Drives
    By GTJim in forum Marketplace Discussion
    Replies: 4
    Last Post: 05-04-2013, 12:05 PM
  3. Nema 34 Stepper Drives,
    By drumsticksplinter in forum Gantry/Router Machines & Building
    Replies: 7
    Last Post: 03-04-2013, 04:20 PM
  4. Toroidal transformer voltages - sanity check needed!
    By m_c in forum General Electronics
    Replies: 16
    Last Post: 03-10-2011, 08:34 PM
  5. Contactor sizing?
    By Swarfing in forum General Electronics
    Replies: 5
    Last Post: 27-12-2010, 08:58 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •