    Use a separate Relay and have the VFD fault Signal turn it on when goes active. Run the E-stop signal thru NO contact.

  2. The Following User Says Thank You to JAZZCNC For This Useful Post:


  3. #12
    new small issue/confirmation : regarding ground, it is best to have one point for all ground right? meaning if chassis of one device is grounded and the whole sheet is grounded, I should not wire the ground connections of other devices if they also ground their chassis right?

    illustration:
    Click image for larger version. 

Name:	IMAG2727.jpg 
Views:	259 
Size:	220.5 KB 
ID:	17269Click image for larger version. 

Name:	IMAG2726.jpg 
Views:	277 
Size:	188.2 KB 
ID:	17270
    in first photo you can see I have connected the power supply chassis to ground wire which goes back to main ground point ( distribution terminals ) so the whole back is grounded. in second photo VFD and power line filter have earth connections but by checking continuity test already these points are connected to back also. so should I skip connecting ground wire to them?

    thank you!

  4. #13
    after some research I realized that all ground contacts should be connected and not rely back panel, anyway I need confirmation of another issue please

    when connecting the VFD with contactor, should all wires ( L,N,Gnd) be connected through the poles or can I just connect the Live with contactor and rest direct from mains power?

    what about the DC output power supply for the drivers?

    thanks!

  5. #14
    Clive S's Avatar
    Lives in Marple Stockport, United Kingdom. Last Activity: 22 Hours Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 3,333. Received thanks 618 times, giving thanks to others 78 times. Made a monetary donation to the upkeep of the community. Is a beta tester for Machinists Network features.
    Quote Originally Posted by Noplace View Post
    after some research I realized that all ground contacts should be connected and not rely back panel, anyway I need confirmation of another issue please

    when connecting the VFD with contactor, should all wires ( L,N,Gnd) be connected through the poles or can I just connect the Live with contactor and rest direct from mains power?

    what about the DC output power supply for the drivers?

    thanks!
    If you really want to connect the VFD through the contactor then just the live would be fine (and not the N or E), but having said that I suppose it depends on the power system to your building as it may be different than the UK.


    I personally would not connect the mains VFD through the contactor but would just connect the signal wire to make it stop.

    The DC output from the power supply should not go through the contactor either .

    Perhaps you should find somebody local to give you some help with this before you get a chance to damage it all or yourself.
    Last edited by Clive S; 20-01-2016 at 12:44 PM.
    ..Clive
    The more you know, The better you know, How little you know

  6. The Following User Says Thank You to Clive S For This Useful Post:


  7. #15
    Quote Originally Posted by Clive S View Post
    If you really want to connect the VFD through the contactor then just the live would be fine (and not the N or E), but having said that I suppose it depends on the power system to your building as it may be different than the UK.


    I personally would not connect the mains VFD through the contactor but would just connect the signal wire to make it stop.

    The DC output from the power supply should not go through the contactor either .

    Perhaps you should find somebody local to give you some help with this before you get a chance to damage it all or yourself.
    hmm well I seem to remember reading that it's safest to turn off power instead of just relying on signal coming out of the devices(drivers,VFDs)
    and the examples in the CSMIO show it this way.

    also I would like to you utilise the software to enable a power on signal

  8. #16
    If you still want to include a contactor to the VFD, then I'm pretty sure that if you hit the e-stop (and turn off the mains power to the VFD) it will not like having the spindle spool down and feeding power back into it when it is not on. Would it damage it? Not sure. But I wouldn't risk it myself.

    I see in one of your earlier posts that you have a braking resistor, which can allow quicker ramp downs (although I've not used mine as it is plenty quick enough without). If you plan to use it I would imagine that killing the power to the VFD would not allow it to use the resistor and it would coast down over a much longer period.

    So if you still want to do this I think you would need a delayed timer on the contactor to switch it off after say 5 seconds, depending on your ramp down parameters. This adds complication, but I know Dean has done this so it is possible. This is in addition to the e-stop logic signal telling the VFD to stop, which you would do first to stop the spindle safely under VFD control.




    I seem to remember reading some time ago that you can be specific and tell the VFD that this is an emergency (not just a regular stop / start command) and it will do an emergency ramp down / stop which is quicker.
    Last edited by routercnc; 20-01-2016 at 10:03 PM.
    Building a CNC machine to make a better one since 2010 . . .
    MK1 (1st photo), MK2, MK3, MK4

  9. The Following User Says Thank You to routercnc For This Useful Post:


  10. #17
    Quote Originally Posted by Noplace View Post
    also I would like to you utilise the software to enable a power on signal
    If your refereing to HV enable then it's not really very suited to this application because it will Kill power to VFD every time you put Mach in reset. Which will be often. This constant stop starting isn't good for the Vfd and will damage it over time.
    Also you won't be able to start cutting straight away after a reset and will need to wait for VFD to power up fully which could be pain.

    If you really do want the VFD turned off then I would have the VFD tied to E-stop but keep it separate from HV enable. Just have HV enable control the drives PSU and the Spindle RUN Command.
    This way when Mach3 is in Reset mode then the VFD stays on but can't started until mach is reset. At which point HV enable turns on the drives and allows spindle RUN signal to reach VFD when needed.

    Think of it has two separate systems working together. E-stop is hardwired and kills everything, HV enable just kills Drives and Run etc but only when mach is in Reset.
    There are many times you'll want some things powered while Mach is in Reset mode. Ie Vacume but at same time your not in E-stop condition.

  11. The Following User Says Thank You to JAZZCNC For This Useful Post:


  12. #18
    thank you guys for the insight and preventing me from making a mistake, I guess the VFD manual confused me because it has some notes about when using a contactor. so in this case is there use for a contactor (for the VFD) at all if controlled through a constant turn on signal?

  13. #19
    appreciate your input on following related subject as well: at the moment the planned way to start/stop the spindle is through input signal coming from CSMIO (the usual way) , in case of problems and I hit E-Stop, naturally CSMIO will disconnect that signal and spindle will stop normally.

    is that sufficient or should I utilise the other input ports of my VFD, it has a total of 8 ports to accept commands from a controller.

    they are as following:
    0 - No Effect
    1 - first multi speed ( references a table in the manual )
    2 - second multi speed ( references a table in the manual )
    3 - third multi speed ( references a table in the manual )
    4 - frequency rises
    5 - frequency decreases
    6 - forward jog
    7 - reverse jog
    8 - forward ( this is what I used before and works fine and is enough to start/stop it )
    9 - reversal
    10 - forward trigger
    11 - reverse trigger
    12 - stop
    13 - freely shutdown
    14 - forced shutdown
    15 - forced inversal
    16 - counter is cleared
    17 - counter input
    18 - program run reset
    19 - external fault
    20 - external reset
    21 - accelerate and decelerate - time choosing first ( references a table in the manual )
    22 - accelerate and decelerate - time choosing second ( references a table in the manual )
    23 - accelerate and decelerate pause
    24 - force ACI passage effective


    I don't understand most of them but its a direct copy-paste from the manual.

    so is it worth doing a setup where one of those functions is triggered during E-Stop? maybe the stop or external fault? hehe feels like overthinking things

  14. #20
    Quote Originally Posted by Clive S View Post

    Looking good though. Not sure you need two 24V power supplies.
    The CSLabs documentation says "If you use in the system such inductive loads as electromagnets, solenoids, electromagnetic clutches – it is recommended to use separate 24V power supply for the mentioned receivers and separate for CSMIO / IP-S."

    This to me suggests that you only need one power supply if you are just switching small loads, such as relays, and a decent size capacitor across the power inputs would remove any ripple, which might cause problems.

    I do not intend to go the extra expense of a second power supply unless absolutely needed.

    Cheers,

    Rob

Page 2 of 2 FirstFirst 12

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Electric motorbike racing
    By Jonathan in forum General Discussion
    Replies: 46
    Last Post: 16-08-2016, 03:28 PM
  2. PSU Assistance
    By CNCStudent in forum General Electronics
    Replies: 13
    Last Post: 05-08-2015, 07:07 PM
  3. FOR SALE: 240v decent electric filter
    By DrNik in forum Items For Sale
    Replies: 3
    Last Post: 16-03-2015, 12:30 PM
  4. ES-D1008 + CSMIO/IP-S wiring
    By Matt81 in forum CS-Lab (CSMIO)
    Replies: 3
    Last Post: 03-05-2014, 10:56 PM
  5. NEW MEMBER: Tunisien request for assistance
    By ali hedi in forum New Member Introductions
    Replies: 0
    Last Post: 01-06-2009, 05:37 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •