    First thing is you don't want to connect any voltage on the CPU to voltage on the vfd. Also I don't have any info on the CPU5A4E.

    If you selected pin17 on the CPU to be 0-10v using the jumper, then as you say connect that to vfd pin 9 (ADC1+)
    Connect CPU pin 25 to vfd pin 10 (0V). The only thing to watch here is, have you used the correct GND terminal on the CPU. Sometimes a particular 0V is associated with the 0-10v, output so just check that.

    This is the tricky part now. Normally the inputs to vfd terminals 3,4,5 are supplied by external relays, but I can't see another terminal associated with OUT TOOL terminal 1 of the CPU to act as a pair of relay contacts.
    Without further info about the CPU5A4E I can't advise anything more.

    Here's a picture of the vfd connections.

    Click image for larger version. 

Name:	G110.jpg 
Views:	2038 
Size:	123.2 KB 
ID:	14586
    Last edited by EddyCurrent; 04-02-2015 at 12:52 PM.
    Spelling mistakes are not intentional, I only seem to see them some time after I've posted

  2. #2
    You can connect the cpu directly to the vfd. If you go onto Berts Eding cnc website and look at the cpu5a flyer, the link is at the bottom of the page, it shows the possible connections.
    If you are really stuck then email Bert and he will help you out.

  3. #3
    Now I see why you mentioned the solid state relay. Personally I would not be connecting the TOOL output directly to the vfd, I would attach a relay between TOOL and GND on the CPU (looks like you would need an external 24V supply), then I would connect the Normally Open contacts of that relay between vfd terminals 6 and 3 (then the vfd would have to be configured by it's firmware so that the input meant RUN FORWARD.
    The main reason for using a relay, and it's the same with PLC outputs, is that it's easier and cheaper to change a knackered relay than it is to replace a knackered controller or PLC, etc. Volt Free contacts as they are called is the way to go for me. For similar reasons I would not be using the 24V supply from the vfd to drive a relay, it only supplies 50mA max.
    Last edited by EddyCurrent; 04-02-2015 at 06:15 PM.
    Spelling mistakes are not intentional, I only seem to see them some time after I've posted

  4. #4
    Hi all,

    Sorry for the late reply, been working.
    I have attached the layout that I think I may go with.

    The external 24v supply seems like a good idea.
    I have already added a 5v supply for the cpu5 board.

    Thanks for the help.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	00001.jpg 
Views:	758 
Size:	78.5 KB 
ID:	14631  

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Tool magazine access and the Siemens CNC Sinumerik controls
    By cossiegaz in forum Siemens (Sinumerik)
    Replies: 6
    Last Post: 05-11-2015, 10:14 PM
  2. Ecostep 200 Controller
    By cncland in forum Motor Drivers & Controllers
    Replies: 0
    Last Post: 14-11-2014, 07:43 PM
  3. Poorly siemens inverter, wont switch on.
    By jonisonvespa in forum Spindles & Drive Motors
    Replies: 7
    Last Post: 06-12-2012, 04:45 PM
  4. FOR SALE: Controller Box for sale
    By lateAtNight in forum Items For Sale
    Replies: 12
    Last Post: 04-03-2012, 10:17 AM
  5. Controller Box
    By M250cnc in forum Motor Drivers & Controllers
    Replies: 1
    Last Post: 21-11-2010, 01:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •