View Full Version : Huanyang setup help



Pugwas
26-09-2022, 07:10 PM
Hi all, just trying to set up a 4kw 380v VFD for controlling the speed of a spray booth extract fan, 3 phase 1440 rpm. out of the box using the rotary knob the max speed I am getting is about half what it was when direct on line, help would be appreciated. The manual is very difficult to take in.

JAZZCNC
29-09-2022, 03:38 PM
Hi all, just trying to set up a 4kw 380v VFD for controlling the speed of a spray booth extract fan, 3 phase 1440 rpm. out of the box using the rotary knob the max speed I am getting is about half what it was when direct on line, help would be appreciated. The manual is very difficult to take in.

You need to supply more info for us to be able to help, such as the model # of VFD Huanyang makes many different models and any parameters you have changed or set up. Also, details on the Motor plate would help. ie Voltage, current, etc.

Also, are you sure it's a 380V output VFD.? Most are 240 single-phase inputs with 240V 3-phase output. Not many provide 240v input with 380v output and I don't think Huanyang makes one but could be wrong on that.!

Pugwas
29-09-2022, 05:18 PM
You need to supply more info for us to be able to help, such as the model # of VFD Huanyang makes many different models and any parameters you have changed or set up. Also, details on the Motor plate would help. ie Voltage, current, etc.

Also, are you sure it's a 380V output VFD.? Most are 240 single-phase inputs with 240V 3-phase output. Not many provide 240v input with 380v output and I don't think Huanyang makes one but could be wrong on that.!

Hi Jazzcnc, The VFD is 3 phase in and 3 phase out (380v) 4kw and brand new. Motor is 4kw 420v 50hz 1420 rpm 8.5 Amps, I did a factory reset on the VFD which changed the parameters from 400 Hz to 50
The motor speed can now be controlled but only via the up/down arrows, when I change the setting to be controlled via the rotary knob the motor will only ramp up to half speed. Using it with the arrows but would be better if I could use the knob

Lee Roberts
12-10-2022, 08:36 PM
We need that model number or a link to the manual @Pugwas if you still need help...

Pugwas
12-10-2022, 10:26 PM
We need that model number or a link to the manual @Pugwas if you still need help...

https://www.ebay.co.uk/itm/383807374664?mkcid=16&mkevt=1&mkrid=711-127632-2357-0&ssspo=CFPfzQzYQLO&sssrc=2349624&ssuid=QVbu34yeRcK&var=&widget_ver=artemis&media=MORE

This is what I purchased

Doddy
13-10-2022, 07:44 AM
What supply are you providing to the power-input to the VFD?

That link suggests a 380VAC(400VAC, UK) 3-phase supply is required.

Pugwas
13-10-2022, 07:55 AM
What supply are you providing to the power-input to the VFD?

That link suggests a 380VAC(400VAC, UK) 3-phase supply is required.

Yes it’s a 3-phase supply, no neutral.