Re: Spindle being awkward.
Stick a meter across the 0-10V and see what that says?
If you're getting voltage drop then it's the output from your BOB so stick the meter across the power supply to the BOB and see what that's doing.
- Nick
Re: Spindle being awkward.
Need more info.
Parallel port or Motion controller.?
What spindle speed controller/BOB.?
What terminals have you connected to on VFD.?
Pics always help.!
Re: Spindle being awkward.
Thanks Nick will do that now and see if thats the issue.
Mick
Re: Spindle being awkward.
Thanks Dean
I have Ess connected to cheap bob similar/same to the ones Emvio Eng recommend.
This picture shows spindle running 12000rpm 4.14 volts at the vdf connections, so looks to me like the relay is misbehaving ?
Sorry despite trying for half an hour I cannot get pics to upload, if needed will try from my house later.
Mick
Re: Spindle being awkward.
PS have checked connections FOR-DCM and V1-ACM checked and double checked.
When rapiding around there is no volt drop.
Mick
Re: Spindle being awkward.
have you set the Pulley ratios.?
Re: Spindle being awkward.
Dean
Pulley no4 max speed 24k ratio 1
Mick
Re: Spindle being awkward.
Have set decel quite high and under mdi stops quick it is the same under jog and program.
Re: Spindle being awkward.
This might help I am getting 23.5v across the FOR connector on the vdf when I press jog.