Re: Fuling DZB200 Inverter
What have you changed. How do you have it wired. The spindle you have seems to be a 2 pole motor
In the manual I don't see a parameter to change the number of poles
From the manual:-
13. About Applicable Motor
1) The standard motor used is the 4-pole squirrel cage asynchronous induction motor. If other kind of
motor is used, please be sure to select the applicable inverter according to the rated current of the motor,
and please consult us if the user wants the inverter to drive the permanent magnetic synchronized motor.
Re: Fuling DZB200 Inverter
Hi thanks for replying.
I have the 240v supply connected as follows:
Live - T connection
Neutral - R connection
Earth
The spindle is connected to U, V & W and also earth
Re: Fuling DZB200 Inverter
A quick Google of GDZ-23 suggests it's a 3 phase motor which will therefore need a different inverter.
Re: Fuling DZB200 Inverter
hmm strange, this was the original inverter/VFD and spindle that was delivered with the machine?
Re: Fuling DZB200 Inverter
Quote:
Originally Posted by
dougie8
hmm strange, this was the original inverter/VFD and spindle that was delivered with the machine?
That dose not mean that they are correct but a lot of VFD's you can change the number of poles.
I would have thought that it should run but not correctly using 4 poles and therefore not be suitable with that spindle. Those spindles require 400 hz and standard motors run on 50 hz.
Re: Fuling DZB200 Inverter
Quote:
Originally Posted by
Kitwn
A quick Google of GDZ-23 suggests it's a 3 phase motor which will therefore need a different inverter.
Yes all these spindles are 3 phase and that's why they a run with a VFD which changes single phase to 3 phase. The VFD is correct.
Dougie, these Fulling VFD's are a pain to setup, I had the same problem with the current machine I'm building and I've fit 100's.
To be honest I can't remember the settings but I do have the written down at work and will check them out for you on monday.
I will scan the manual today to see if it jogs my memory.
1 Attachment(s)
Re: Fuling DZB200 Inverter
Thanks, I've attached a photograph of the nameplate from the inverter the manual was downloaded from another forum Attachment 28248
Re: Fuling DZB200 Inverter
Thanks Jazzcnc, I was getting a bit confused by the previous guys replies as the inverter was still fitted and wired into the BOB in the machine when I took delivery, the pervious owners had only disconnected the spindle.
very much appreciated
Re: Fuling DZB200 Inverter
Ok I've just looked at the manual and I remember the parameter that sorted my issues was F1.0 I can't remember what it's set too but this was the game changer parameter so try changing it to 0 or 1 and see what happens. I think you need to restart the VFD for changes to take affect.