Re: Control Schematic Advice
Shit forgot to reply to your email Jim Sorry I will now. Or better still email me your number and I'll give you a ring as it much easier over the phone.
Re: Control Schematic Advice
I've not looked in great detail but the following stand out to me-
Home switches should be wired NC if you're looping them together.
.
Do you really need to use two seperate relays for limits and E-stops?
I know it can be nice to know what's just caused everything to grind to a halt, but it does add cost and complexity for little practical benefit when you could simply wire the limit swithced in series with the e-stops. And if you're unsure what's caused things to stop, hitting the limit overide should tell you if it's a limit or e-stop issue.
Re: Control Schematic Advice
Quote:
Originally Posted by
m_c
I've not looked in great detail but the following stand out to me-
Home switches should be wired NC if you're looping them together.
They are NC switches but there's a bigger problem here.? The A2 on K1 relay doesn't go to 0V it goes to 15-70V on the BOB so it won't ever turn on.!
Also don't kill power to the BOB leave it running.
Ring me Jim.
Re: Control Schematic Advice
Quote:
Originally Posted by
JAZZCNC
They are NC switches
I know they are, but they're shown wired NO in the diagram...
Unless Jim is planning on them only being activated when in the home position, then it's wrong.
.
Good catch on the BOB power. You really don't want to kill that.
Re: Control Schematic Advice
Quote:
Originally Posted by
m_c
I know they are, but they're shown wired NO in the diagram...
Unless Jim is planning on them only being activated when in the home position, then it's wrong.
Erm ye go on then I'll let you have it on technical merit. .:hysterical: . . . . But I think it's just that Jim found the first symbol of a switch to use and thats why he wrote NC so we'd know which switch type.?
Re: Control Schematic Advice
You ain't getting nothing on technical merit!
.
He's got COM, NC, and NO shown, but has used the COM & NO in the diagram.
Re: Control Schematic Advice
Quote:
Originally Posted by
m_c
You ain't getting nothing on technical merit!
.
He's got COM, NC, and NO shown, but has used the COM & NO in the diagram.
Sorry MR my mistake didn't notice you said Home switches I was looking at Limit switches. Obvioulsy your correct and I'll go sit in the naughty corner. .Lol
Re: Control Schematic Advice
:highly_amused:
Attachment 11732
Re: Control Schematic Advice
Quote:
Originally Posted by
m_c
Yes Moray that's quite fitting to me this last week has lack of sleep along with diminishing eye sight have made for some Dunce moments.!! . . . . I may just make a sign like that for the door. . Lol