Re: About my Thoroid transformer...
Any connection between the bolt head and the chassis will result in a shorted turn
but if its fitted in a low profile metal enclosure
then it may be possible for the top to be deformed and touch the bolt head if pressure is applied !
Attachment 26393
John
Re: About my Thoroid transformer...
Quote:
Originally Posted by
john swift
Any connection between the bolt head and the chassis will result in a shorted turn
but if its fitted in a low profile metal enclosure
then it may be possible for the top to be deformed and touch the bolt head if pressure is applied !
Attachment 26393
John
How about the lower end? The nut will be in contact there right?
Re: About my Thoroid transformer...
the lower end is OK as the chassis , bolt and top mounting disk don't form a complete turn around the toroidal core
its only when you close the loop by connecting the mounting disk to the chassis by a conductor outside the core
John
Re: About my Thoroid transformer...
Quote:
Originally Posted by
john swift
the lower end is OK as the chassis , bolt and top mounting disk don't form a complete turn around the toroidal core
its only when you close the loop by connecting the mounting disk to the chassis by a conductor outside the core
John
Allright, thanks! :thumsup:
When were at it, what type of fuses would you use for a PSU?
Re: About my Thoroid transformer...
Quote:
Originally Posted by
JW1977
Allright, thanks! :thumsup:
When were at it, what type of fuses would you use for a PSU?
For a toroidal transformer feeding a rectifier/smoothing capacitors you'll need a time delay (T) fuse as the switch on current surge can be VERY large.
However if you have a fairly constant power drain you can reduce the surge by fitting a NTC thermistor in series
Re: About my Thoroid transformer...
Any idea what the transformers VA rating is ?
As a toroidal transformer inrush current is very large
I would not be supprised if you need a fuse 3 or 4 times what the VA rating would indicate
if you have a 600VA transformer
you may have to use a HRC 10A mains fuse (HRC = High Rupture Capacity)
and check what type of circuit breaker is supplying the radial circuit your mains socket connected to
for example
a type B breaker trips at 3 to 5 times the full load current operating time 0.04 To 13 Sec
a type C breaker trips at 5 to 10 times the full load current operating time 0.04 To 5 Sec
John
PS
if the transformer is large enough you may have to consider using an inrush current limiter
some examples here -
https://sound-au.com/articles/inrush.htm
PPS
more details of a Soft-Start Circuit
https://sound-au.com/project39.htm
Re: About my Thoroid transformer...
Quote:
Originally Posted by
Voicecoil
For a toroidal transformer feeding a rectifier/smoothing capacitors you'll need a time delay (T) fuse as the switch on current surge can be VERY large.
However if you have a fairly constant power drain you can reduce the surge by fitting a NTC thermistor in series
Allright, i have to keep looking into that...
Re: About my Thoroid transformer...
Quote:
Originally Posted by
john swift
Any idea what the transformers VA rating is ?
As a toroidal transformer inrush current is very large
I would not be supprised if you need a fuse 3 or 4 times what the VA rating would indicate
if you have a 600VA transformer
you may have to use a HRC 10A mains fuse (HRC = High Rupture Capacity)
and check what type of circuit breaker is supplying the radial circuit your mains socket connected to
for example
a type B breaker trips at 3 to 5 times the full load current operating time 0.04 To 13 Sec
a type C breaker trips at 5 to 10 times the full load current operating time 0.04 To 5 Sec
John
PS
if the transformer is large enough you may have to consider using an inrush current limiter
some examples here -
https://sound-au.com/articles/inrush.htm
PPS
more details of a Soft-Start Circuit
https://sound-au.com/project39.htm
Yes, its 800VA. Got some Reading to do about this, thanks!