Re: Fuling DZB200 Inverter
Quote:
Originally Posted by
MarshaJusa
From what I'm seeing the VFD model you have is designed for three phase to three phase... The R, S, T terminals are for three phase, if it were designed for single phase input it would have L and N.
Marsha
That is not correct. There are plenty of these inverters that has a three phase input and you can use any of the three phases to connect the single phase to.
IE. R,S or R,T
Re: Fuling DZB200 Inverter
Quote:
Originally Posted by
MarshaJusa
From what I'm seeing the VFD model you have is designed for three phase to three phase... The R, S, T terminals are for three phase, if it were designed for single phase input it would have L and N.
Marsha
No It's not. All the Fulling VFD's and many of the other Chinese VFD's come with R S T inputs and you just connect to any 2 of them for Single phase. They also accept 3 phase input.
I have just fitted the same VFD to single phase supply.