Re: N0VUSUN and Mitsubishi-D700-SC
Quote:
Originally Posted by
JAZZCNC
Does that mean your working.?
HI,
Got the diodes and all wired up but i am not getting the spindle to spin up from mach 3, it seems like the NOVUSON controller is not switching the relay on through mach3.
i have the 24v supply to the relay,the ov from the power supply goes to grd1 on the s axis and the ov from output 1 from the s axis goes back to the relay.
can anyone help me with the settings as i have tried various one from both manuals
thanks Dave
Re: N0VUSUN and Mitsubishi-D700-SC
I think you said previously that you could manually spin up the spindle by grounding the control into the VFD, so the VFD and the programming is okay?
This should be do-able. If you can post a photo of the wiring to the relay (try to get as much in there as you can), and do you have a DMM (multi-meter) - can you measure the output-1/S-Axis output for spindle On/Off.
EDIT:
I *expect* (though might be wrong) that the Out-1 will be measured at around 24V with the spindle off, and "some" volts - maybe 8-16 with the spindle "On". If so, if you can report back.
Re: N0VUSUN and Mitsubishi-D700-SC
Have you enabled and setup the Output1 in Mach3 and then selected output1 in spindle control.?
Also, does the plug-in have any settings that need setting.? . . .I've no idea on this as never used this controller but usually, there is a spindle section in most plug-ins that needs to be eneabled or setup.
Re: N0VUSUN and Mitsubishi-D700-SC
Quote:
Originally Posted by
Doddy
I think you said previously that you could manually spin up the spindle by grounding the control into the VFD, so the VFD and the programming is okay?
This should be do-able. If you can post a photo of the wiring to the relay (try to get as much in there as you can), and do you have a DMM (multi-meter) - can you measure the output-1/S-Axis output for spindle On/Off.
EDIT:
I *expect* (though might be wrong) that the Out-1 will be measured at around 24V with the spindle off, and "some" volts - maybe 8-16 with the spindle "On". If so, if you can report back.
hi i will check this out
thanks
Re: N0VUSUN and Mitsubishi-D700-SC
i have noticed that the led on the relay lights up but dim and does not click in when the spindle is switched on in mach 3
the relay works 100% if i wire it direct to the power supply it clicks in and closes the contacts.
the relay is wired direct to the +24v on the power supply and the ov ground from the power sully goes to crd on the novusun...the out1 from the s axis goes to the relay for the OV
Re: N0VUSUN and Mitsubishi-D700-SC
Quote:
Originally Posted by
JAZZCNC
This should help, it's basic setup with a diode across the relay to stop back feed from blowing the output up. See Doddy's rough top sketch for diode details.
Attachment 27775
This is the wiring i have followed
1 Attachment(s)
Re: N0VUSUN and Mitsubishi-D700-SC
Attachment 27830
this is the diagram i have followed
so between GRD1 and OUT1 on the s axis there should be no voltage, this circuit is closed by the controller when spindle is switched on in mach3
Re: N0VUSUN and Mitsubishi-D700-SC
Quote:
Originally Posted by
Daveo
i have noticed that the led on the relay lights up but dim and does not click in when the spindle is switched on in mach 3
the relay works 100% if i wire it direct to the power supply it clicks in and closes the contacts.
the relay is wired direct to the +24v on the power supply and the ov ground from the power sully goes to crd on the novusun...the out1 from the s axis goes to the relay for the OV
Just checking that you do have a DC relay and NOT AC type :encouragement:
Re: N0VUSUN and Mitsubishi-D700-SC
Quote:
Originally Posted by
Daveo
i have noticed that the led on the relay lights up but dim and does not click in when the spindle is switched on in mach 3
the relay works 100% if i wire it direct to the power supply it clicks in and closes the contacts.
the relay is wired direct to the +24v on the power supply and the ov ground from the power sully goes to crd on the novusun...the out1 from the s axis goes to the relay for the OV
Good, this is very useful. The relay you have (MY4N-J) is a 24VDC relay, to answer Clive. That the LED on the relay illuminates, dimly, when "on" answers the question of whether the driver is configured correctly - from memory the driver is a very simple thing that doesn't really respect the ports/pins settings in Mach3. So that looks good. You've tried manually energising the relay and that works as expected - so VFD wiring and settings are good. This leads me back to my questions, and a hunch that I have.
First one - photos of the relay, I wanted to check if you've wired the diode correctly, but if you hadn't then you wouldn't be able to manually energise the relay (not without blowing the 1n4001... not entirely unlikely if it is wired the wrong way around).
Secondly, the voltage on the out-1 pin on the NVEM. If it is low, at 0V or maybe up to 2-3V then I'd say the opto-coupler output (internal to the NVEM) is switching as designed. But that would give you a bright LED. If, as I'd rambled about earlier, it doesn't switch effectively (low CTR) then the opto-coupler driving the NVEM output will have a high resistance, and the terminal voltage at OUT1 will be some proportion of the 24V supply. The higher the terminal voltage, the lower the voltage across the coil (and the internal LED) and the less energy to switch the relay. My question of the measured voltage - if above more than a few volts then I don't believe the NVEM is effectively switching the relay and we have to look at a current amplifier. I (or many others here) can help you sort that.
5 Attachment(s)
Re: N0VUSUN and Mitsubishi-D700-SC
hi all
back down the shed to sort this out
photos attached
Attachment 27841
Attachment 27839
Attachment 27840
Attachment 27842
Attachment 27843
ok i get 24v upto the relay base when i click the spindle in mach3 but the relay is not clicking in as if there just was not enough amps