21-11-2016 #1
Hi All!
I have a customer that is getting a recurring fault on his stepper drive where the motor terminals are burning out. There are 2 identical drives and motors on the machine but only one drive has this problem. I haven't had chance to put a meter on the motor but just wondered if this is a common fault. The have replaced the drive 3 times now.
Best regards,
John.
-
21-11-2016 #2
Well, you can take the "Pass" sticker off that drive...
Slightly more seriously, that's definitely just the output pins for one coil that are burnt, which suggests a wiring or motor fault downstream of this point. Seems very unlikely to be due to the driver itself. Intermittent short circuit? Pinched insulation somewhere that causes a momentary short when the machine is in certain positions?
-
21-11-2016 #3
Thanks Neale,
The customer hasn't reported any other fault with the drive (apart from the fact that they have to change the drive every 6 months!) I'll see if I can get any more info from him. It's a 6 hour round trip to site just to stick the meter on but I'll see if I can get their maintenance guy to take some initial measurements and check the cabling.
-
22-11-2016 #4
Thats what you get with cheap shity drives that don't have protection built in.!! This will 99% be motor fault either due to wiring or phase trouble.
Considering it's such long trip IMO it would be cheaper to change out motor/Drive and wiring. While at it fit good quality drives that will protect them selfs.
Personanlly I couldn't sleep at night worrying next time it might not stop at burning the connector and start on burning the building.!!
-
The Following User Says Thank You to JAZZCNC For This Useful Post:
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Control box wiring: cables, terminals, connectors etc.
By eurikain in forum General ElectronicsReplies: 10Last Post: 07-11-2015, 07:34 PM -
AC servo motor to replace a 3 phase induction motor on a mill spindle.
By rnr107 in forum Spindles & Drive MotorsReplies: 2Last Post: 23-04-2014, 03:14 PM -
CY cable terminals
By kingcreaky in forum Marketplace DiscussionReplies: 15Last Post: 26-03-2014, 08:24 AM -
servo motor as spindle motor
By Scott in forum General DiscussionReplies: 1Last Post: 03-10-2010, 06:42 PM
Bookmarks