  1. #1
    Stan's Avatar
    Lives in Bicester, United Kingdom. Last Activity: 24-07-2017 Has been a member for 4-5 years. Has a total post count of 13.
    Hi,
    Thanks for replying,
    yes you are correct what comes to maual and wiring, all is there.
    But real life is different.
    L goes to R or S or T
    Earth goes to E(9)
    And N?
    I can't connect N to R or S or T
    R,S,T is phase not Neutral
    It tripped my Fuse straight, I've tried, twice.
    Thanks for replying. Stan

  2. #2
    Cropwell is quite right - you connect live to one of the RST terminals and neutral to one of the other two. It doesn't matter which. My HY inverter has been working beautifully for a few years like this, just like many others. If your MCB or RCD is tripping, there must be a fault elsewhere - can you describe a bit more what the inverter is plugged in to?

  3. The Following User Says Thank You to Neale For This Useful Post:


  4. #3
    Quote Originally Posted by Neale View Post
    Cropwell is quite right - you connect live to one of the RST terminals and neutral to one of the other two. It doesn't matter which. My HY inverter has been working beautifully for a few years like this, just like many others. If your MCB or RCD is tripping, there must be a fault elsewhere - can you describe a bit more what the inverter is plugged in to?
    Neale and Rob of are correct but there has been a post on the forum that some VFDs have a problem with this (and I can't remember) but I think it is something to do with an internal EMC filter that can be disconnected to stop this.

    This might have been the post http://www.mycncuk.com/threads/6593-...ghlight=filter #6
    Last edited by Clive S; 02-01-2017 at 11:46 AM. Reason: added link
    ..Clive
    The more you know, The better you know, How little you know

  5. The Following User Says Thank You to Clive S For This Useful Post:


  6. #4
    Are you connecting to a dedicated MCB ? I know when I first started using (any) inverters in my garage they would "always" trip the main house supply. I got my sparky mate round and he said "yeah, it will always pop the fuse unless you fit a (can't remember what he said) ???? Anyway, he done his thing and fitted a dedicated socket in the garage which I now run all my VFD's from, problem solved. Just to add, if I plug a VFD into any of the other normal sockets, they instantly trip the main supply in the house.

  7. The Following User Says Thank You to needleworks For This Useful Post:


  8. #5
    Stan's Avatar
    Lives in Bicester, United Kingdom. Last Activity: 24-07-2017 Has been a member for 4-5 years. Has a total post count of 13.
    Hi, thanks to all who replied.
    It's all over now.
    I've waisted £299.
    My VFD is burned out.
    Unfortunatelly I wan't so lucky as many of you with my VDF Huanyang.
    It's all about wiring.
    RST is life only, you can't conect N neutral to it, it will burn as mine.
    Thank you all for your support, I appreciate it.
    Click image for larger version. 

Name:	IMG_0066.JPG 
Views:	4250 
Size:	536.1 KB 
ID:	20143Click image for larger version. 

Name:	IMG_0063.JPG 
Views:	1879 
Size:	477.8 KB 
ID:	20144Click image for larger version. 

Name:	IMG_0059.JPG 
Views:	947 
Size:	411.3 KB 
ID:	20145Click image for larger version. 

Name:	IMG_0064.JPG 
Views:	1344 
Size:	564.4 KB 
ID:	20146Click image for larger version. 

Name:	IMG_0061.JPG 
Views:	3086 
Size:	468.0 KB 
ID:	20147Click image for larger version. 

Name:	IMG_0067.JPG 
Views:	866 
Size:	441.1 KB 
ID:	20148

  9. #6
    Quote Originally Posted by Stan View Post
    Hi, thanks to all who replied.
    It's all over now.
    I've waisted £299.
    My VFD is burned out.
    Unfortunatelly I wan't so lucky as many of you with my VDF Huanyang.
    It's all about wiring.
    RST is life only, you can't conect N neutral to it, it will burn as mine.
    Thank you all for your support, I appreciate it.
    Click image for larger version. 

Name:	IMG_0066.JPG 
Views:	4250 
Size:	536.1 KB 
ID:	20143Click image for larger version. 

Name:	IMG_0063.JPG 
Views:	1879 
Size:	477.8 KB 
ID:	20144Click image for larger version. 

Name:	IMG_0059.JPG 
Views:	947 
Size:	411.3 KB 
ID:	20145Click image for larger version. 

Name:	IMG_0064.JPG 
Views:	1344 
Size:	564.4 KB 
ID:	20146Click image for larger version. 

Name:	IMG_0061.JPG 
Views:	3086 
Size:	468.0 KB 
ID:	20147Click image for larger version. 

Name:	IMG_0067.JPG 
Views:	866 
Size:	441.1 KB 
ID:	20148
    You can indeed connect L to R, S or T and N to one of the other two. That would NOT burn up the VFD, that is the normal way of connecting it. But it assumes that you have a VFD which is for Europe, not for the USA. Is that the case? I mean maybe the seller sent you a unit which is for the USA market.

  10. The Following User Says Thank You to A_Camera For This Useful Post:


  11. #7
    Stan's Avatar
    Lives in Bicester, United Kingdom. Last Activity: 24-07-2017 Has been a member for 4-5 years. Has a total post count of 13.
    Hi.
    The seller send it the VDF for Europe wiring.
    I live in uk, we have 240 volt 50/60 Hz.
    Also I've contacted ebay seller, he send me the same youtube wideo as everybody saying here, including you (A_Camera) that I should conect L wire to R and N neutral to any S or T and earth to E.
    Which I did, and what has happend, no idea.
    All my wiring at home is correct.
    I have fuse board, one fuse 32 A type2 M6 is going to my garage, wire is 2,5mm, strong enought . Also on fuse board is 80A RCD.
    Maybe the RCD 's is problem?Click image for larger version. 

Name:	IMG_0068.JPG 
Views:	637 
Size:	141.7 KB 
ID:	20149
    Last edited by Stan; 02-01-2017 at 06:32 PM.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Mach3 Controlling Huanyang HY02D223B 2.2KW VFD
    By Mad Professor in forum Spindles & Drive Motors
    Replies: 34
    Last Post: 01-10-2016, 10:21 AM
  2. help connecting a pot to huanyang vfd 2.2
    By edgas10 in forum General Electronics
    Replies: 15
    Last Post: 14-08-2016, 06:45 PM
  3. Huanyang hy02d223b frequence convertor problem
    By frans cop in forum Motor Drivers & Controllers
    Replies: 3
    Last Post: 14-07-2015, 10:33 AM
  4. Huanyang VFD control plugin for Mach3, USB RS-485
    By JayPunchbuggy in forum Spindles & Drive Motors
    Replies: 19
    Last Post: 15-05-2013, 08:00 PM
  5. huanyang vfd 2.2 error E.CO.A
    By edgas10 in forum General Electronics
    Replies: 0
    Last Post: 01-07-2012, 08:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •