OK - I'm goint to try knock up a more complete schematic, and see what you think
-
18-04-2017 #3
-
18-04-2017 #4
Don't like this setup because you don't have latching safety circuit. How you have it now soon as you release the E-stop the system becomes active again regardless if the fault is cleared or not.
Personally, I would run the E-Stop thru Master relay wired so forms latch. This then controls the Killing of power to high powered devices like Drives, Vfd etc. Then informs PMDX E-stop occurred which then does the Rest and turns off its Outputs. The Master Relay can only be Reset by pressing Momentary Button and will only allow the Relay to reset if all faults are clear.
The E-stop circuit can then be run using 24V giving better noise immunity.
-
19-04-2017 #5
Ok, But latching or not, the software that is running the machine will go into reset condition the second it receives an E-stop or limit switch touched, until someone physically pushes the reset button in the software, and then clicks on start again in the software. So regardless of weather the E-stop remains latched or not, The PDMX will not activate anything again as the software is in reset active mode? A latching circuit is adding another layer of buttons I have to press to get the machine started again.
What do you think about the load I was placing on the K2 relay? All i did was look at the rated Watts, or Amps per motor and figure out what that would be at 240 Volts ( 100% conversion) to guess the load at max drain for everything on? It says 10A max in the manual
-
19-04-2017 #6
A key rule is never to trust software!
What size of machine is this?
Personally, I'd ensure the e-stop circuit removed all power to anything that moves directly, which if I remember correctly from the PMDX manual, the BOB will kill all outputs as soon as the E-stop signal is lost. However, I'd add an extra relay (the onboard relay is probably not ideally rated for handling PSU start-up surges) controlled directly by the E-stop circuit (adding a reset/latch is reasonably easy - they are a legal requirement for commercial use, but hobbyist use you can do whatever you want as long as it's only you that's going to risk getting injured), which controls power to the drives.
If the E-stop directly controls the main power relay, then you can use an extra set of contacts in the relay to switch the BOB E-stop input. Unless you're using more than about one KW/KVA of power supply, I'd use a common DIN rail mounted DPDT 10A relay. RS part numbers are 488-2610 for the relay, and 803-376 for the socket to give you an idea of the type - other sources are available.
Having the main drive power supply active without the BOB active is not a problem, as the BOB/software should prevent any motion from occurring. The big problem arises when you rely on the software to kill things, and the reason you want to kill things is because the software isn't doing what it should, so you really want to make sure the E-stop kills everything, even if the computer/software is doing it's very best to not stop things.Avoiding the rubbish customer service from AluminiumWarehouse since July '13.
-
The Following User Says Thank You to m_c For This Useful Post:
-
19-04-2017 #7
-
22-04-2017 #8
JAZZ, most of my faults have been detected by controllers etc, but regarding the 882 error loop..... Do you know, or does anyone know 100% that it is the main motor DC power that needs to be cycled in order to clear the fault?
How are guys doing this? just Cutting the Active line before the ac/dc converter using a low voltage DC press button through a relay?
Redone Schematic, can't decide where to put the E-stop. In the pic, it overrides everything, and turns the pdmx off, but keeps the motion controller on as I don't want to cut that off.
Option 2, is rely on the pdmx safety E-stop circuit, as it will cut power to spindle / motion commands / dust extractor and coolant. then I can on / off the motors if needed to clear fault separately?
I'm normally no where near this machine when it's running, as the jobs are hours long, and I rely on it turning itself off when it faults, not sitting there watching it non stop - as such the e-stop rarely gets used as I'm not there ( No-one is )Last edited by dachopper; 22-04-2017 at 05:41 PM.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
CSMIO-IP/S Driving Relays directly
By cropwell in forum CS-Lab (CSMIO)Replies: 10Last Post: 02-01-2017, 01:40 AM -
Which PSU and drivers do I need ?
By eurikain in forum General ElectronicsReplies: 10Last Post: 18-08-2015, 11:44 AM -
not enough current for relays?
By Boyan Silyavski in forum General ElectronicsReplies: 17Last Post: 17-08-2015, 10:05 AM -
FOR SALE: pdmx 107 spindle speed control board
By dazza in forum Items For SaleReplies: 0Last Post: 08-05-2014, 02:58 PM -
question about relays
By frankman in forum General ElectronicsReplies: 3Last Post: 23-01-2012, 07:47 AM




Reply With Quote

Bookmarks