Thread: Lenze i500 Inverter
Threaded View
-
20-04-2017 #3
there are 2 options not to open it.
1 use higher protection current 500mA
2 connect before protection device if possible
reason as jazzcnc mentioned EMC filter
Poslano sa mog MI 5 koristeći Tapatalk
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Very Sick Lenze 534 Controller
By Ricardoco in forum Motor Drivers & ControllersReplies: 32Last Post: 09-09-2020, 11:19 PM -
2.2KW 3HP Inverter help
By adamh in forum Spindles & Drive MotorsReplies: 8Last Post: 31-07-2015, 09:21 AM -
Broken transformer in Lenze Speed Control 530.
By Samuel59 in forum Motor Drivers & ControllersReplies: 3Last Post: 23-04-2014, 12:22 PM -
WANTED: Electrical Box for inverter
By badgerman in forum Items WantedReplies: 1Last Post: 28-09-2013, 11:08 PM -
Lenze 534
By Ricardoco in forum Milling Machines, Builds & ConversionsReplies: 12Last Post: 29-07-2012, 09:59 PM
Bookmarks