    Quote Originally Posted by Nickhofen View Post
    I am thinking to place the parts that way in the control box,will it be any problem with the positioning of VFD?
    If I remember correctly people puts shielede cables to the signal wires ,wires that goes to controllers, motors etc. right?
    Click image for larger version. 

Name:	46498937_295025274456788_8663817126231932928_n.jpg 
Views:	367 
Size:	71.4 KB 
ID:	25119
    I personally prefer the VFD outside of the control box. The spacing on the drives are fine I tend to use cat3 twisted for the signal wires and CY 4 core for the motors the shield grounded to the star point at one end only
    ..Clive