The fact the motors are still trying to move, tells us the drivers are still trying to move the motors, which leaves only two possibilities. Either there is something mechanical jamming, or there is some kind of glitch in the step pulse stream causing the motors to stall.
Where did you source the ballscrews?
Something like a bit swarf in the nut, can cause these kinds of symptoms. It just occasionally gets dragged between a ball and the screw, causing things to jam. Stop motion, swarf gets moved out the way, and things start running perfectly again. Only way to find out if this is the case, is to dismantle the nuts and clean them.
Noise could cause a glitch resulting in a sudden deceleration/acceleration, which could be enough to cause the motor to stall. However I'd still expect that amount of noise to cause other problems. Key things I'd be checking/double checking, is any shielding goes back to a star point, and you've not introduced any ground loops anywhere.Avoiding the rubbish customer service from AluminiumWarehouse since July '13.
-
28-07-2017 #23
With the shielding, is that all the shielding, including spindle braid and stepper shielding together at one end on mains power earth, or just together?
-
10-08-2017 #24
Hi guys,
My suspicions were correct, the culprit is EMI coming from the spindle, but now that I have replaced all of the cables...... I need some electronically minded advice.
The spindle is leaking current to the entire machine when it is powered somehow.
Inside the 2.2KW inverter, I have the house power connected to R /T on the left for active / neutral, and Ground on the far right.
Then I have the spindle power on U/V/W in the middle.
The shielding on the spindle cable is not connected to anything at the Inverter end, but it overlaps onto the metal plug at the Spindle end - could this be the cause?
The other possible issue is that this spindle does not have an earth - aside from it's power return cable.... If I did run an earth wire attached to the spindle or aluminium Z axis block, can I just plug that into the house power earth inside the inverter box, or could that cause some kind of fault/loop?
The question is, is the charge coming from the shielding getting charged, and because it's touching the outside of the metal plug, it's then charging the machine, or the lack of a spindle frame Earth is now somehow causing the issue
-
10-08-2017 #25
Ok First make sure the machine frame is earthed to the star point in the control box, make sure the screen on the spindle cable is earthed at one end only (solder a wire to the screen and ground it to the spindle body)
Are all your other cable screens grounded to the star point (In the control box you should have only one point where everything is grounded to)..Clive
The more you know, The better you know, How little you know
-
10-08-2017 #26
Ok.... I disconnected the Spindle power cable braided sleeve so it is now fully insulated at both ends, and so is not physically touching the metal spindle plug either.
With the spindle turned on at 18,000 rpm, I have a 40 Volt ac signal generated, between the Spindle/Machine, and the spindle power cords' Braided Sleeve, at 9,000 hz. The machine ran without issue.
So - should I run an earth from the braided sleeve to house . power inverter earth at one end.... I don't see how this would dissipate electricity though as it's an AC signal effectively being generated by EMI.
2. I will probably run another earth wire back from the spindle to the House earth now - to stop electric shocks in the case of other failures.....
If I have the AC leaking braided sleeve earthed with the inverter / house earth, and also conect an earth from the spindle to the inverter / house earth, I could be back at square 1 as the spindle could get some of the AC?
-
10-08-2017 #27
In the control box, I have main 220Volt house power earthed to the corner of the mounting plate, The Stepper Drivers are bolted to the plate, and the Torroidal Transformer is also bolted to the plate.
Then I have a single earth wire coming off that same corner to a small ACDC transformer, and another single wire that goes off then splits to 4 and is the AC earth for my woodchip / 2 x pond pumps and Spindle power inverter.
So I should earth the spindle + Spindle sleeve to earth in the inverter? or back to star?
From DC transformer - all that suff plugs directly into the stepper drivers etc....
-
10-08-2017 #28
Try downloading some manuals for good quality VFDs to see how they recommend grounding.
Typically the screen would be connected to the earth point at the VFD. Then the VFD earth connected to the star point.
Whether the screen gets connected to the motor varies. I'd be inclined to try it with and see how things run, as having the spindle well grounded is recommended from a safety point.
Ideally you want to avoid ground loops, however sometime they're unavoidable. Having them in the screen of a power cable isn't likely to cause problems. The problems occur when you get a ground loop in signal wire screen, as that's when you start introducing noise into control circuits.Avoiding the rubbish customer service from AluminiumWarehouse since July '13.
-
10-08-2017 #29
-
11-08-2017 #30
Ok , Thanks Clive / M_C
I ended up running a separate ground from the spindle all the way back to the star, and from the sleeve all the way back , and another from the inverter power feed all the way back
The shock I was getting on the Z axis has moved to a different area of the frame ..... WTF !
I don't really understand how AC voltage is detected, but what I noticed is that I seem to have 12 Volt AC between my machine and the workshop floor, although the freq jumps. When I power up the anxillary devices, ( water pumps, spindle powered but not turning, and woodchip extractor on but not turning, the A/C jumps up to a constant 105-110 Volts 60Hz. I get a tingle touching the machine frame bearfoot after that.
Does this seem like an earth leak in the shed somewhere?
The machine frame was earthed to the same star point as the inverter / Dc transformer / spindle / spindle sleeve. I tried discnnecting it as I'm trying to figure out where the zapping is coming from.
All I know is that with the machine on and the DC steppers motoring, there is no problem and no zapping.
With the spindle relay on..... and spindle turning there was big zapping when the spindle rotated.... that is fixed , but now there is a smaller underlying zap that is on when the A/C power is on regardless if the devices are turning or not.
Should my stepper motor power sleeves also go to the same A/C ground? they are currently not connected? ( insulated both ends )Last edited by dachopper; 11-08-2017 at 07:49 AM.
Thread Information
Users Browsing this Thread
There are currently 4 users browsing this thread. (0 members and 4 guests)
Similar Threads
-
Help with Problem X axis Stepper Please
By howser37 in forum Gantry/Router Machines & BuildingReplies: 53Last Post: 09-02-2017, 06:31 PM -
Which single stepper for long axis?
By Boyan Silyavski in forum Motor Drivers & ControllersReplies: 0Last Post: 24-05-2015, 08:39 AM -
Connecting BOB one axis to 2 stepper drivers
By Noplace in forum General ElectronicsReplies: 8Last Post: 10-02-2015, 11:56 AM -
Z axis error woes
By HankMcSpank in forum Machine DiscussionReplies: 46Last Post: 18-02-2012, 03:07 PM -
The dreaded task of workshop tidying!
By m_c in forum Milling Machines, Builds & ConversionsReplies: 0Last Post: 26-03-2011, 08:07 PM
Bookmarks