Thread: Selecting the right driver
Hybrid View
-
01-09-2009 #1
So let’s take the PM542's (PDF), they have a Typical Supply Voltage of 36v with a MAX of 50v.
A late forum member told me I should supply them at the max (50v) is this the correct thing to do? Or would it be better to supply the driver with the Typical Rated Voltage?
I want to get the best speed I can from the motors, will supplying the driver at the MAX voltage mean the motor will also receive a higher voltage and give me better speeds?
If we take the Nema23 3Nm motor (PDF), the document said:
Bipolar Parallel 2.73v, 4.2a, 3Nm
So from that, i take it for the Motor to run at 3Nm Holding Torque it will require from the driver 2.73v and 4.2a ?
The other question i have is about the Motor, when a phase is "in use" is the Volts and Amps it is pulling from the driver divided by the amount of wires coming from the motor?.Me
-
01-09-2009 #2
The max voltage is 50V, but over this voltage and the driver will trip into error, so i suggest to use a 40V PSU.
Forget the 3Nm holding torque, it is not the holdiong torque that you need, it is the torque while moving.
Also a stepper driver is a constant current device, so the motor does not pull current, the driver controls the current.
Visit Us: www.automationshop.co.uk
-
30-03-2010 #3
I've been saying that for years, it's the torque against speed graph that counts, the one with the voltage next to it :whistling:
OTOH why mess around? I used all sorts of stepper drivers until Gary came up with his 220VAC jobbies and I haven't looked back since. Just make sure your motors can handle the lowest amp setting and fit a griddle to one axis so you can cook breakfast whilst cutting. Oeufs a la swarf. Crunchy
-
05-09-2009 #4
Lee, Gary has answered some of your points but let me throw in my 2p worth.
Electronic devices should never be run at the absolute maximum voltage quoted. Depending on the circuit this might either be the protective trip voltage or the voltage at which damage can occur due to internal breakdown of the device (which then results in high peak currents frying the device unless there is an external curent limit). In this instance its the protective trip. If you were to feed the driver with 50v there is the possibility that back-EMF from the motor when pushing energy back into the power supply (on the overrun/braking cycle) would cause the power supply voltage to rise and trip which would be inconvenient at best and catastrophic to the workpiece at worst! If your power supply is really good, with a regulation of better than 2% then you might get away with running it at 48v or so. But I'd stay below 45v on these drivers.
From the motor torque curves on Gary's site you can see that at 500steps/sec (150rpm) the torque is already down at 2Nm. Below 150rpm the torque will tend towards the holding torque but the relationship isn't linear. You will notice from these torque curves that the curve for 60v/4.3A is flatter/more linear than that for 40v/4.3A but the difference isnt really apparent below 2500steps/sec (750rpm). In other words if you are never going above 750rpm on the motor then 40v will perform as well as 60v. If you have only got 40v drivers then this information can be used to factor any gearing to keep the motor in the sweet spot.
The stepper driver is a constant current device. whatever the motor winding resistance the driver will never allow more than the rated current through the winding. For a driver set at 4.2A this is the maximum it will allow. The voltage rating of a stepper motor is irrelevant, it is merely the steady state voltage across the windings at the rated current due to the winding resistance. With a chopper or PWM current controller it has no meaning as the driver will switch the drive voltage on and off at high frequency to maintain the average current at the set value. Since it is being switched the winding inductance has a part to play as this controls the rate at which the current can change in the winding. This is where the higher voltage comes into play as a higher voltage can 'force' a higher current in a shorter time therefore maintaining the torque at higher speeds.
I'm guessing the meaning of your last question... refering to the data sheet for the motor again, when wired bipolar parallel the first phase has A and /C connected together and /A and C connected together. When that phase is energised, 4.2A of current flows from the driver along the connecting wire to the A + /C junction where it splits - 2.1A into each winding - and recombines at the /A + C junction, where 4.2A of current flows back to the driver. Therefore every one of the 4 wires connecting the driver to the motor carries 4.2A and needs to be rated for that.
Hope this helps...
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Stepper Motor Driver - cheap similar to ArcEuro 4.2A Bi-Polar Stepper Motor Driver
By craynerd in forum Motor Drivers & ControllersReplies: 1Last Post: 16-03-2014, 07:29 PM -
BOBCAD V24, Selecting issue on boundry & geomatry
By craigrobbo in forum BobCAD-CAMReplies: 1Last Post: 14-05-2012, 02:56 PM -
Which stepper driver
By Colin Barron in forum Motor Drivers & ControllersReplies: 0Last Post: 25-09-2010, 08:33 PM -
DIY Driver Cards
By malik sohail in forum Electronic Project BuildingReplies: 3Last Post: 27-12-2009, 10:41 PM -
Driver box
By John S in forum General ElectronicsReplies: 1Last Post: 21-06-2009, 12:46 PM
Bookmarks