Hooray, a small success!
I have now got the motor running under load, for this I had to set P72. Unfortunately, the motor now runs very rough in operation. Can someone help me with the torque settings P70, P71 and P72?

Greetings Marc
Something is not right with the fundamental settings. P72 is just for additional torque at low speed. I did not use mine in the end as there was plenty of torque when I did some test drilling.

How is this wired to the motor ? Delta pattern I assume ? Is this wired correctly at the motor end ?

How many poles? I assume 2 poles from the rpm ? Is this set correctly ?

What is the max current set to P76? Maybe this is too low and the P72 is helping you out but it is not the way to solve it.

Check all connections are tight.