I am running 5 NEMA 23 motors from a 750VA toroid and there is a fair bit of inrush when it switches on (lights dim momentarily). I needed a 10A type D MCB in the end to avoid it tripping out.
1000 or 1200 VA is going to be interesting.

Do you need that much as the steppers do not take anything like the rated current added together