  1. #1
    Hi Charlie

    I am surprised the the charge pump output has failed again

    I would of thought the combination of the diode added across the relay coil to control the back emf
    and the 27 ohm resistor to limit the current if the relay was ever short circuited
    would of protected the FET

    Can you measure the voltage between the CHP O1 and -24V terminal

    when the output should be ON and OFF

    and if possible the voltage across the 10K resistor on the PCB

    knowing the voltage between the 74HC14 GND pin 7 and output from pin 2
    will help

    I would expect it to be 0V when OFF and +3 to +5V when ON

    from the FET data
    Gate Threshold Voltage = min 1.5V to max 2.5 V

    John
    Last edited by john swift; 16-11-2019 at 12:51 AM. Reason: add ref to Gate Threshold Voltage

  2. #2
    Quote Originally Posted by john swift View Post
    Hi Charlie

    I am surprised the the charge pump output has failed again

    I would of thought the combination of the diode added across the relay coil to control the back emf
    and the 27 ohm resistor to limit the current if the relay was ever short circuited
    would of protected the FET

    Can you measure the voltage between the CHP O1 and -24V terminal

    when the output should be ON and OFF

    and if possible the voltage across the 10K resistor on the PCB

    knowing the voltage between the 74HC14 GND pin 7 and output from pin 2
    will help

    I would expect it to be 0V when OFF and +3 to +5V when ON

    from the FET data
    Gate Threshold Voltage = min 1.5V to max 2.5 V

    John
    Sorry for the late reply, so I managed to check a couple of voltages before the battery died on my volunteer again...really should remember to turn it off! It reads 9v when off and 24v when on when the relay is connected. but I had a brainwave and it works so unless you say it's a bad idea I'm going to stick with it...
    The charge pump only activates the relay when the software is active and reset state is inactive, the problem was that it wouldn't then shutoff on reset or estop so I have used an opto isolated relay on another output which is the true state of reset and settable in uccnc. This means that the relay isn't active unless the software is active and reset is not. It also protects the AXBB against any other issue causing the charge pump failure..

    Sent from my SM-G920F using Tapatalk

Thread Information

Users Browsing this Thread

There are currently 4 users browsing this thread. (0 members and 4 guests)

Similar Threads

  1. Advice on a charge controller please :)
    By blackburn mark in forum General Electronics
    Replies: 23
    Last Post: 04-05-2020, 07:28 PM
  2. CNCDrive AXBB super deal?
    By driftspin in forum CNCdrive (UC100, UC300ETH)
    Replies: 18
    Last Post: 16-03-2019, 10:10 PM
  3. Not sure where the fault lays
    By terry1956 in forum Vectric
    Replies: 5
    Last Post: 20-02-2019, 11:28 AM
  4. fault testing
    By Palletlad in forum General Computing
    Replies: 2
    Last Post: 09-02-2018, 05:51 PM
  5. Jun-Air Compressor Fault
    By jamesgates1000 in forum General Discussion
    Replies: 5
    Last Post: 02-12-2017, 07:59 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •