    Quote Originally Posted by chillybo View Post
    Thanks Jazz. Have just had a NPN normally closed proximity switch delivered from Amazon. Im guessing then that with this device I would set the input for it to active high?
    No that would be Active Low.
    Because the type is N/C Mach sees the signal all the time(High) and when signal disappears (low) the pin goes active. So it's (Active Low)
    If it was N/O type it would be the reverse. The pin is low and goes Active when the signal is High. (Active high)

    Word of caution with the IP/M and it's inputs. They are Non-isolated which means the don't tolerate being miss wired so before you go connecting anything up to them be sure you fully understand what your doing, they don't take prisoners.!

  2. The Following 2 Users Say Thank You to JAZZCNC For This Useful Post:


Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Proximity wiring for limit switches, safety relay and a contactor
    By CharlieRam in forum General Electronics
    Replies: 15
    Last Post: 02-06-2019, 11:18 PM
  2. EMC2 home/limit switches... only acting as limit?
    By vputz in forum LinuxCNC (EMC)
    Replies: 4
    Last Post: 15-10-2014, 09:51 AM
  3. Help needed with proximity switches
    By Boyan Silyavski in forum General Electronics
    Replies: 6
    Last Post: 11-07-2014, 03:29 AM
  4. Proximity Switches
    By kingcreaky in forum General Electronics
    Replies: 20
    Last Post: 23-10-2013, 01:30 PM
  5. Proximity Sensors as Limit Switches ?
    By Lee Roberts in forum General Electronics
    Replies: 5
    Last Post: 03-10-2009, 07:04 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •