Thread: Kit's Machine

Page 4 of 7 FirstFirst ... 23456 ... LastLast
  1. #31
    Quote Originally Posted by Doddy View Post
    Kit, your last response does concern me - if you remove the "electromechanical galvanic isolation module" from the Z-limit input to the bob, and simply connect this input to the local 0V, is it still noisy? If so you're down to BoB/Cable/PC.
    I haven't actually removed the EGIM but it does strap the input to ground. I have made some interesting measurements though. Some screen grabs from the oscilloscope are very telling...

    trying to accurately the voltage on the earthed case of the machine is a bit difficult since earth is meant to be the refference voltage. this is measured on the case of the LinuxCNC PC with the scope earth floating. 10mS/div. 4V/div.
    Click image for larger version. 

Name:	2021-02-20_103615.png 
Views:	1891 
Size:	63.0 KB 
ID:	29569

    Slightly less scary, this is one of the parallel port pins pins referenced to the PC case. 1mS/div. 0.2V/div. None of the motors were running so there's not controll data on the pin.
    Click image for larger version. 

Name:	2021-02-20_103400.png 
Views:	1785 
Size:	59.4 KB 
ID:	29570

    Most scary is another floating measurement of the metal frame of the CNC router itself. 1mS/div. 4V/div.
    Click image for larger version. 

Name:	2021-02-20_104840.png 
Views:	1835 
Size:	61.6 KB 
ID:	29571

    So my theory that that the intereference is going out on the mains cable of the VFD is probably wrong, it's more likely coming from the spindle itself.
    The spindle is connected using screened 3-core cable with the screen connected to the mains earth inside the VFD and to the body of the spindle and hence to the frame of the machine.
    So why does the mains filter on the VFD do some good? Dunno. Why does plugging the VFD into another mains socket stop all trips occuring and allow me to use the machine as normal? Dunno.

    I have improved the earth bonding of the Z axis and gantry to the base frame but the above measurements are after that was done. For the present I'm just going to get on and use the machine as it is for it's intended purpose and hope for the best but, as I've said before, if this hobby turns commercial I shall want to upgrade the controller to something less flakey.

    Kit
    Last edited by Kitwn; 20-02-2021 at 10:51 PM.
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  2. #32
    Throw the scope and the bloody BOB in the bin and buy an AXBB-E you tight bugger, all your problems solved.!. . . Simplizzzz
    -use common sense, if you lack it, there is no software to help that.

    Email: [email protected]

    Web site: www.jazzcnc.co.uk

  3. #33
    Quote Originally Posted by Kitwn View Post
    The spindle is connected using screened 3-core cable with the screen connected to the mains earth inside the VFD and to the body of the spindle and hence to the frame of the machine.
    If you have earthed your frame then surely you have created an earth loop by connecting the VFD cable shield at the spindle end.? I don't earth the spindle end and never have noise problems.
    -use common sense, if you lack it, there is no software to help that.

    Email: [email protected]

    Web site: www.jazzcnc.co.uk

  4. #34
    phill05's Avatar
    Lives in Derbyshire  UK, United Kingdom. Last Activity: 13 Hours Ago Has a total post count of 302. Received thanks 30 times, giving thanks to others 13 times.
    We had a problem at one stage that sounds close to what you have, we had the screen connected at both ends, to remedy took off screen at spindle end now left with 3 +Earth, ( 4-core CY cable) connected spindle to VFD, at the VFD end the screen was stripped back and finished at star point in cabinet, VFD was fitted in same cabinet on the same power line in.
    Been running for four years no problems.

    Phill

  5. #35
    Quote Originally Posted by JAZZCNC View Post
    Throw the scope and the bloody BOB in the bin and buy an AXBB-E you tight bugger, all your problems solved.!. . . Simplizzzz
    It's just possible you may be right.
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  6. #36
    Quote Originally Posted by JAZZCNC View Post
    If you have earthed your frame then surely you have created an earth loop by connecting the VFD cable shield at the spindle end.? I don't earth the spindle end and never have noise problems.
    Connecting the spindle cable braid to the spindle body has a lot to do with safety, there being plenty of volts available to spoil your day, though making sure the machine body is well earthed should solve that. Interesting point made earlier about grounding emissive cable screens at both ends and receptive ones only at one end. The principle of reciprocity may not support this however.

    I have already got UCCNC running in demo mode on my laptop and have confirmed that delivery to Australia will not take too long so I can see his happening soon. How does UCCNC compare to LinuxCNC? How easy is it in practice to set up auto-squaring for a two-motor axis?
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  7. #37
    Quote Originally Posted by phill05 View Post
    We had a problem at one stage that sounds close to what you have, we had the screen connected at both ends, to remedy took off screen at spindle end now left with 3 +Earth, ( 4-core CY cable) connected spindle to VFD, at the VFD end the screen was stripped back and finished at star point in cabinet, VFD was fitted in same cabinet on the same power line in.
    Been running for four years no problems.

    Phill
    Thanks Phill. I might try this, though at the moment I just want to start making some bits with a working machine, which is what I now seem to have. I expect that I will soon have to bite the bullet and upgrade to an AXXB-E and UCCNC to make things more reliable. It will also be intereststing to see what difference this makes to the maximum speed of the machine and the surface finish as ONE OF THE USEFUL THINGS I'VE LEARNED FROM MY OSCILLOSCOPE (subtle hint there you notice ) is that the pulse timing from LinuxCNC and it's parallel port are far from perfect. Long ago I set up a test and measured the step pulse interval at 125uS with frequent (approx 1 in 8) pulses at either 100 or 150uS (always +- 25uS). That's a pretty dramatic error and cannot be good for best performance.
    I have now got the mechanical side of the machine working quite well, as far as my limited experience can tell, so an upgrade to the control side is worthwhile. I will keep yours and Dean's comments in mind when that rebuild gets underway.

    Kit
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  8. #38
    It's been working quite well recently. I've had some frustrations with the T-nuts I'm using for clamping but have that issue (mostly) sorted after having to dissasemble the baseboard twice.

    The real clincher has been the old LinuxCNC PC which has suddenly shut itself down a couple of times and did this yesterday in the middle of a long trochoidal cut of some clock gears. After some cleaning and reassembly the PC has now stayed on all night but it's not really reliable so I've bitten the bullet and ordered an AXBB-E and a software licence for UCCNC. Balazs has confirmed they have one in stock so it should be here quite soon. Funny thing is that after moving 5000Km from the remote wilds of Western Australia to 5 minutes outside the third largest city in Tasmania DHL still class this as a 'remote' location so they're going to sting me 48EU for delivery.

    Any useful words of wisdom regarding the installation of the new card will be welcome, especially any tips from those who have already switched from LinuxCNC to UCCNC.

    Kit
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  9. #39
    To be fair mate, "the third largest city in Tassie" makes it sound like a bustling metropolis. Isn't Devonport basically the size of Truro?

    Oh and if you get a chance to pop into the House of Anvers, I still have vivid dreams of those Belgian waffles....
    Last edited by AndyUK; 29-03-2021 at 05:24 PM.

  10. #40
    Quote Originally Posted by AndyUK View Post
    To be fair mate, "the third largest city in Tassie" makes it sound like a bustling metropolis. Isn't Devonport basically the size of Truro?

    Oh and if you get a chance to pop into the House of Anvers, I still have vivid dreams of those Belgian waffles....
    I'm not sure it's quite that big. But that isn't the point!!!

    Actually Balasz said that DHL treat most of Australia other than Sydney as remote. The way the world is right now I quite like 'remote', though not as remote as our former home in Exmouth, WA. Compared to that Devonport really is a bustling metropolis, close to the heart of all things civilised, including the House of Anvers which is a popular destination, especially with my wife.

    Kit
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

Page 4 of 7 FirstFirst ... 23456 ... LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Newbie Machine Build Log (Fancy Machine)
    By Fancy in forum Gantry/Router Machines & Building
    Replies: 2
    Last Post: 18-09-2018, 06:15 PM