Thread: Cncst4060
Hybrid View
-
04-09-2020 #1
Now, spindle speed control. This assumes F002 = 1, also. (You've not confirmed this yet)
If you do confirm its set to 1, then changing to 3 should, according to the manual, give you speed control through the built-in pot. Try that and report back.
Will do it now bud
-
04-09-2020 #2
On the vfd we have changed the setting to F002 But nothing happens and on F001 the e stop came on on the vfd
-
04-09-2020 #3
I'm reading this as, "On the VFD we've checked the setting of F002 and confirmed that this was set to 1. We've changed this from 1 to 3 and set this, but testing with the VFD switch ON, the potentiometer on the front panel still has no influence on the Spindle"
and I do not understand "and on F001 the e stop came on the vfd" - There is no "e stop" indicator on the VFD, is there? You shouldn't change F001 (I don't believe I suggested that you should). The settings/values are taken from the manual thet I'd linked...