Thread: Cncst4060

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Now, spindle speed control. This assumes F002 = 1, also. (You've not confirmed this yet)
    If you do confirm its set to 1, then changing to 3 should, according to the manual, give you speed control through the built-in pot. Try that and report back.

    Will do it now bud

  2. #2
    On the vfd we have changed the setting to F002 But nothing happens and on F001 the e stop came on on the vfd

  3. #3
    Quote Originally Posted by petesos View Post
    On the vfd we have changed the setting to F002 But nothing happens and on F001 the e stop came on on the vfd
    I'm reading this as, "On the VFD we've checked the setting of F002 and confirmed that this was set to 1. We've changed this from 1 to 3 and set this, but testing with the VFD switch ON, the potentiometer on the front panel still has no influence on the Spindle"

    and I do not understand "and on F001 the e stop came on the vfd" - There is no "e stop" indicator on the VFD, is there? You shouldn't change F001 (I don't believe I suggested that you should). The settings/values are taken from the manual thet I'd linked...

    Click image for larger version. 

Name:	Screenshot 2020-09-04 at 18.37.18.png 
Views:	1920 
Size:	88.6 KB 
ID:	28800