    Since nobody seems to want to buy my old lathe due to it's current dual voltage setup, I'm thinking about changing it so it runs solely of 240V.

    The spindle is easy enough to sort, but the turret is more of a problem.
    It uses a 600W 3 phase 110V motor, which is currently powered via a 3 phase 415->110V transformer, then two interlocked contactors for forward/reverse.

    If I was to power it with a VFD, am I correct in thinking, all I need to do is change the rated motor voltage setting in the VFD from 230V, to 110V?
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  2. #2
    Chaz's Avatar
    Lives in Ickenham, West London, United Kingdom. Last Activity: 2 Weeks Ago Has been a member for 9-10 years. Has a total post count of 1,600. Received thanks 110 times, giving thanks to others 69 times.
    Not sure about that. In my experience (limited), the VFD's voltage output is pretty much set. For example in my 9100 VFD, they offer some tuning of the output but its like 380-410, not anything that would allow me to half the voltage.

    That said, why not try one, set it down 110V and use a dummy load and measure what it outputs.

  3. #3
    Are you sure that's the reason it isn't selling? The way I see it, you are proposing to spend money to replace a perfectly acceptable and well understood method of powering the 110V motor with something which is probably less reliable, more complex and difficult to replace or fault-find at a later date.

    Kit
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

  4. #4
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Quote Originally Posted by Chaz View Post
    Not sure about that. In my experience (limited), the VFD's voltage output is pretty much set. For example in my 9100 VFD, they offer some tuning of the output but its like 380-410, not anything that would allow me to half the voltage.

    That said, why not try one, set it down 110V and use a dummy load and measure what it outputs.
    VFDs vary voltage according to frequency, so at below motor rated speed, they're reducing voltage anyway, it's just that I'm not sure it'll be as simple as changing a single parameter.
    If I had a standard VFD surplus, I would try it and see, but I've not just now.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  5. #5
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 3 Days Ago Forum Superstar, has done so much to help others, they deserve a medal. Has been a member for 9-10 years. Has a total post count of 2,908. Received thanks 360 times, giving thanks to others 8 times.
    Quote Originally Posted by Kitwn View Post
    Are you sure that's the reason it isn't selling? The way I see it, you are proposing to spend money to replace a perfectly acceptable and well understood method of powering the 110V motor with something which is probably less reliable, more complex and difficult to replace or fault-find at a later date.
    I've had a couple people interested, but they've not had access to 3 phase, which is why I'm thinking about changing it.
    Currently it needs 3 phase for the spindle and turret, and single phase for the controller and servos.

    I am considering keeping it, as it can do things it's replacement can't, but I would like to simplify how it's powered regardless.
    Avoiding the rubbish customer service from AluminiumWarehouse since July '13.

  6. #6
    Quote Originally Posted by m_c View Post
    I've had a couple people interested, but they've not had access to 3 phase, which is why I'm thinking about changing it.
    Currently it needs 3 phase for the spindle and turret, and single phase for the controller and servos.

    I am considering keeping it, as it can do things it's replacement can't, but I would like to simplify how it's powered regardless.
    For some reason I failed to notice that this is a 3-phase motor even though you wrote that twice! Must press the 'ON' button on my brain before writing comments in future!

    Kit
    An optimist says the glass is half full, a pessimist says the glass is half empty, an engineer says you're using the wrong sized glass.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. 110v 3 phase for baruffaldi turret
    By jonnydeen in forum Motor Drivers & Controllers
    Replies: 17
    Last Post: 06-09-2020, 11:48 PM
  2. Replies: 21
    Last Post: 19-01-2017, 01:49 PM
  3. Porter Cable 75182 Router on 110V site transformer.
    By James123 in forum Porter Cable Routers
    Replies: 6
    Last Post: 19-11-2014, 05:42 PM
  4. motor power and chinese spindles power HELP
    By DigiSoft in forum Spindles & Drive Motors
    Replies: 5
    Last Post: 17-09-2013, 12:17 AM
  5. Stepper Motor Power Question
    By boldford in forum Gantry/Router Machines & Building
    Replies: 0
    Last Post: 17-07-2012, 09:40 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •