Smiffy,
It's not that difficult. The frequency describes the rotational speed of the magnetic field provided by the controller to the motor... so top whack of 400Hz = 400 cycles/second, or 24000 cycles per minute.
However, motors are typically 2 pole or 4 pole - describing either a magnetic N/S pair (180 degrees apart) or a N/S/N/S 2-pair (90 degrees apart). When considering the actual RPM of the rotor, divide the rotational speed by the number of pole-pairs. So, 24000 cycles/min = 24000 RPM for a 2-pole motor, or 12000 RPM for a 4-pole motor.
That's why you'll find single-phase mains AC motors at 1500RPM or 3000RPM, depending on if they're 4-pole or 2-pole (respectively).
Some/many spindle controllers will allow you to program the number of pole-pairs - that's necessary to determine the RPM from the frequency.
-
24-03-2022 #2
But a slight wrinkle is that induction motors have to run slightly below the synchronous speed, at say 85 - 95%, so the actual speed will be slightly lower than that set by the inverter frequency. The difference is the "slip", and your VFD might allow this to be programmed as well.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Single phase input variable frequency inverters XSY-AT1
By oldshooter in forum Motor Drivers & ControllersReplies: 12Last Post: 31-07-2020, 08:04 PM -
Suggested PWM frequency for a minimal Novamill conversion
By GND in forum Denford MillsReplies: 5Last Post: 04-04-2020, 12:50 AM -
High frequency vfd 1500hz
By assadi in forum Spindles & Drive MotorsReplies: 0Last Post: 28-08-2018, 04:12 PM -
Configuring Altivar 12 frequency regulator for PID control
By vesilp in forum Spindles & Drive MotorsReplies: 4Last Post: 28-01-2017, 04:26 PM -
Display bezel
By Robin Hewitt in forum General ElectronicsReplies: 1Last Post: 18-08-2009, 12:09 PM
Bookmarks