08-09-2023 #2
Wow that is a massive overkill. You can simply get a timer relay and a metal clad resistor from CPC or Farnell to do the job. I used a Finder timer relay - I think it was this one last time https://cpc.farnell.com/finder/80-21...0timer%20relay
Worst thing is, Rod Elliott doesn't seem to understand what causes the periodic / random current surge when the transformer is connected. The effect is called "remanence". During normal operation, there is a fairly large AC magnetising current flowing in the primary due to the primary inductance, resulting in an alternating magnetising flux in the core. This is independent of the load on the output. At the instant when you disconnect the mains voltage, much of the magnetising flux at that instant remains (hence "remanence"). If you tried to dismantle the transformer at this point, you'd find the cores were magnetised and wanting to stay together. The magnitude and polarity of the remanence is random, as the interruption is not synchronised to the voltage waveform. When you now come along and reconnect the mains voltage to the primary, you superimpose a magnetising current / flux on top of the remanent flux. Depending on the instant at which that reconnection happens, you can now end up with a higher flux than you would ever see in normal operation.
The steady state magnetising flux of most transformers is actually very close to the saturation flux of the core, so it doesn't take much additional flux to saturate them, which is what causes the random massive inrush currents. The current during saturation is only limited by the voltage, winding resistance and the impedance of the mains network. And these large surges are a random function of the instantaneous voltages at connection and disconnection of the mains, which is why you only seem them from time to time rather than at every power on. You may have wondered why they only happen every so often.
To implement a resistive soft start on the transformer primary, you need to use a resistor that is small enough in value to drive the magnetising current close to its equilibrium value but high enough to limit the current if there is saturation during the first few cycles. This is why the soft start resistor value needs to be selected according to the specific transformer. For the range 1kW - 3kW, I have found values in the range 3 to 22 Ohms work well and the delay timer only needs to be set to a second or so.
-
The Following User Says Thank You to Muzzer For This Useful Post:
Thread Information
Users Browsing this Thread
There are currently 6 users browsing this thread. (0 members and 6 guests)
Similar Threads
-
Soft limits over ride
By Pilsbury in forum Machine DiscussionReplies: 2Last Post: 01-12-2022, 01:36 PM -
Is there a 'standard' base design, or does everyone start from scratch?
By Richard in forum Gantry/Router Machines & BuildingReplies: 3Last Post: 27-10-2017, 09:13 AM -
Soft Start Advice
By GTJim in forum General ElectronicsReplies: 18Last Post: 15-01-2015, 08:47 AM -
RFQ: Panels cut from soft plywood
By Rockeyes in forum Projects, Jobs & RequestsReplies: 0Last Post: 12-04-2013, 04:38 AM -
Simple Current Limiter (LM317)
By Mad Professor in forum General ElectronicsReplies: 14Last Post: 13-07-2009, 10:01 PM
Bookmarks