26-09-2011 #11
If that's at nominal mains voltage it will give you over 48 V at the maximum of +10%; I wouldn't want to go any higher. Did you measure the mains voltage when testing?
Russell.
-
26-09-2011 #12
No.
I seem to have a lack of insulated proves for the multimeter just now, so just measured to make sure the voltage wasn't too high. The Gecko's are good for 50V, so a 6V safety margin should be good enough.
-
27-09-2011 #13
You are probably OK. However, the reason I asked is that the UK mains voltage is 230 V with a tolerance of +10%, -6%. So, if the mains voltage was 6% low when you made the measurement, then the voltage you get at maximum mains voltage will be over 50 V. An unlikely but possible situation.
Russell.
-
27-09-2011 #14
If it's for the Gecko G540 then this will do the job. http://www.airlinktransformers.com/t...with-leads.asp
I've just built a control box for someone using this toroid and It is giving a steady 47V and my mains input voltage is quite high due to the fact I live bang next to the sub station.
I've had it on test know for several weeks and no issues's so far.
EDIT: Doh . . . didn't read all the post's did I.!! . See your sorted.Last edited by JAZZCNC; 27-09-2011 at 09:39 PM.
-
The Following User Says Thank You to JAZZCNC For This Useful Post:
-
28-09-2011 #15
Russell, you've got me curious now!
I'll have to go and find a multimeter with suitable clamps, just to satisfy myself.
Jazz, I'll keep a note of that, as I've got a couple other projects I'd like to do that may involve more G251s.
-
28-09-2011 #16
Another thing to consider is: Did you measure it under load?
A transformer usually specified under full RESISTIVE load. So, when unloaded the voltage increases by the specified regulation figure. I guess you tested it unloaded in which case you are safe. Calculating the output voltage of a transformer/rectifier under mixed capacitive and resistive load is by no means easy. For a one off, your approach of try it and see is the best way.
Russell.
-
03-10-2011 #17
Thread Information
Users Browsing this Thread
There are currently 2 users browsing this thread. (0 members and 2 guests)
Similar Threads
-
screening / glitchy operation - sanity check
By dsc in forum General ElectronicsReplies: 21Last Post: 01-12-2013, 11:35 PM -
Toroidal Transformer
By Carlb1058 in forum General ElectronicsReplies: 7Last Post: 17-08-2013, 06:54 AM -
maximum deflection - sanity check
By dsc in forum Gantry/Router Machines & BuildingReplies: 6Last Post: 11-02-2013, 09:33 AM -
Different voltages on different steppers
By Lovre in forum Motor Drivers & ControllersReplies: 2Last Post: 12-12-2012, 11:28 PM -
sanity check - constant running, loads and more
By dsc in forum Stepper & Servo MotorsReplies: 4Last Post: 26-11-2012, 12:26 PM
Bookmarks