Thread: VFD (?) tripping RCD
Hybrid View
-
27-11-2011 #1
Ah, you did mention that (I've been helping a mate move house today, so am currently a bit tired!).
I'd be more inclined to try it with an ammeter, as that way things are still tied to earth, and give a better idea if it's something slowly building to tripping point, or something causing a more sudden spike. Of course an oscilloscope would be better, but you may as well try with what tools you've got to hand first.
-
27-11-2011 #2
I have so far only tried it with the ammeter. Oscilloscope (http://uk.farnell.com/gw-instek/gds-...our/dp/1563796) goes down to 2mV/div ... so I could in theory use an about 0.5ohm resistor and it'd still show 30mA.
Spindle is still running ... that's been over half an hour. Only difference I suppose is it's now running unloaded, so not going to heat up much unless I restrict the cooling. Not going to try that as I'm a fan of non destructive analysis!Last edited by Jonathan; 27-11-2011 at 12:55 AM.
-
27-11-2011 #3
Assuming you haven't overlooked anything or missed something in the tests you have already done... It sounds similar to a problem I had with radios some years ago. ...
Bring some power from the house or from next door! but bypassing the RCD unit, with a standalone RCD if necessary, (but if you are happy to have a hand in your pocket while disconnecting earths you probably wont want to! lol)
Try plugging each of the suspect items; the VFD? into the extension lead with everything else plugged into the main RCD, as soon as it stops dying or the problem disappears you have the suspect device cornered for further investigation
or... find a way of removing DC from the AC line back to the RCD, or split board supply??
The RCCD you point to; 40amp? is it 30 or 100 mA?Last edited by mocha; 27-11-2011 at 01:54 AM.
-
27-11-2011 #4
Jonathan,
there's been discussion about this recently on the EMC2 mailing list - something to do with filters in the VFD providing a path to earth - which then trips the RCD. So it might not be a fault per se, just the way the VFD is designed to work. I know Andy Pugh and others experienced this issue (and hopefully solved it). He frequents the EMC2 forum - it might be worth asking a question over there:Sorry Jonathan just re-read your post properly - since your set up was working fine for a year this is unlikely to be the cause
Link: EMC2 forums
NathanLast edited by NB70; 27-11-2011 at 10:44 AM. Reason: Read the original post properly
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
VFD Tripping an RCD
By Washout in forum Spindles & Drive MotorsReplies: 13Last Post: 04-09-2017, 02:07 PM -
RCD tripping
By motoxy in forum General ElectronicsReplies: 4Last Post: 23-02-2013, 09:36 PM
Bookmarks