  1. Quote Originally Posted by JAZZCNC View Post
    Not very easy to read labels but I suspect your using the HV option on controller to turn on contactor.?
    Don't use it my self because it's pain in arse.? It will drop the power to drives every time you put mach into reset. This means because the motors jump when powering drives you'll have to home the machine everytime mach goes into reset. Many times that will be ok but there are others when you don't want that. Like when making simple setting change etc.
    I'd just have the E-stop safety relay switch contactor on.

    Couple of small things I see.

    #1 Fuse the Water pump.
    #2 Run water pump 0V thru VFD relay so only comes on when spindle running.

    Regards VFD power then wouldn't get too OCD about it.! The controller will Stop it spinning when see's E-stop so could leave it out of the E-stop system if you like.
    But if you do want to Kill it then use Timer relay which is set to drop power after spindle stops spinning. Personaly I wouldn't bother because the few times you will Kill power while spindle is spinning won't hurt the VFD. Plus the VFD takes several sec's to power down anyway because of Caps. By which time spindle will have stopped.! . . . . . Anyway If Cutter is embedded in your hand you won't really care because you'll passout before VFD powers down.
    Thanks for the Help!

    I have added a fuse to the water pump (not sure what ampage for that yet as haven't chosen a pump yet.)

    I have added another contactor and a switch on the 24v circuit to control the pump and VFD

    I'm not sure what you mean when you say you just have the E-stop safety relay switch the contactor on. Presumably I still want the drive fault signals connected to the pilz?

    Click image for larger version. 

Name:	Circuit Diagram 04 _ 0.jpg 
Views:	1688 
Size:	270.2 KB 
ID:	19469

    Also, I am struggling with grounding the various components. Do I need to connect the motors or drives back to the star ground and if so, how?!

    Also should the earth terminal on the VFD just go back to the earth terminal on the plug or the star ground and should the CSMIO just go back to the star ground or should this also be connected back the earth on the power plug?

    I know similar questions have been asked and answered elsewhere but I'm struggling to piece it all together...

    Thanks guys.
    Last edited by JoeHarris; 18-10-2016 at 01:30 PM.

Thread Information

Users Browsing this Thread

There are currently 356 users browsing this thread. (0 members and 356 guests)

Similar Threads

  1. BUILD LOG: 3 Axis Router
    By GTJim in forum DIY Router Build Logs
    Replies: 8
    Last Post: 22-06-2020, 08:49 AM
  2. 3-Axis CNC Router - For Helices.
    By Dalmango in forum Gantry/Router Machines & Building
    Replies: 4
    Last Post: 08-02-2014, 07:27 PM
  3. BUILD LOG: Wobbly: my first 3-axis router
    By Sodster68 in forum DIY Router Build Logs
    Replies: 8
    Last Post: 20-01-2013, 10:28 AM
  4. 3 axis cnc/router bed
    By dudz in forum Marketplace Discussion
    Replies: 23
    Last Post: 28-12-2012, 09:38 PM
  5. Need 6' x 4' bed, 4 axis router design.. Help..!
    By fasteddy in forum Gantry/Router Machines & Building
    Replies: 29
    Last Post: 17-09-2010, 12:56 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •