    So we were saying mostly the same thing. That's a good start :)

    I think I've worked out where my mental block is for this element at least. I was treating parallel as increasing A rather than decreasing the division of A. In other words, I was thinking of two outputs, each with 50V 625VA. Parallel would make this one output of 50V 1250VA. Rather, I should be looking at it as two outputs of 50V sharing 625VA between them - effectively making it 100V / 625VA = 6.2A. Wiring it in parallel would then have the same VA but divided by less, which has the same end effect as doubling it: 50V / 625VA = 12.5A. When I look at it like this, your previous comments make more sense so I guess I'm on the right track.

    And you wonder why I get jittery with mains power

  2. #2
    Quote Originally Posted by Rogue View Post
    And you wonder why I get jittery with mains power
    This is the secondary winding, no mains there

    The core of the transformer is primarily what determines the power rating, hence why changing the windings from series to parallel cannot change the power rating (VA) you get.
    Old router build log here. New router build log here. Lathe build log here.
    Electric motorbike project here.

  3. Quote Originally Posted by Jonathan View Post
    This is the secondary winding, no mains there

    The core of the transformer is primarily what determines the power rating, hence why changing the windings from series to parallel cannot change the power rating (VA) you get.
    But remember the old adage: Its volts that jolts but Amps that kills... so 70v at 12A still needs treating with respect

  4. #4
    Quote Originally Posted by irving2008 View Post
    But remember the old adage: Its volts that jolts but Amps that kills... so 70v at 12A still needs treating with respect
    I thought the old adage was "Of course it's not live, I checked it just a few miARRRggRGRgrGRGGRGRHHHHH"?

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Denford Triac VMC year 2000 motors spec
    By suesi34e in forum Milling Machines, Builds & Conversions
    Replies: 1
    Last Post: 17-11-2013, 11:44 PM
  2. Advice on spindle inverter spec
    By badgerman in forum Spindles & Drive Motors
    Replies: 12
    Last Post: 15-09-2013, 09:26 PM
  3. Hiwin linear blocks HGW 20 CC - what preload to spec?
    By range3rrr in forum Rails, Guideways & Bearings
    Replies: 1
    Last Post: 24-08-2011, 11:44 PM
  4. FOR SALE: Servo Spec gearbox's ---- Any offer considered
    By Jimmybristol in forum Items For Sale
    Replies: 11
    Last Post: 30-05-2011, 11:04 PM
  5. System spec and Mach3
    By gorbo in forum Computer Hardware
    Replies: 5
    Last Post: 23-01-2011, 03:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •