Soft start for that size of transformer isn't really needed. Just use a zero volt switching SSR (most AC SSR's are), and you shouldn't have any issues.
One thing to note though, is if the SSR fails, it'll likely fail short circuit, so oversize and fuse it to minimise the risk. If you're really concerned, put a mechanical relay in circuit before it, incase anything does happen.
Generally you only fuse the transformer primary side. Any overload on the secondary side should blow the fuse on the primary side. If you oversize the rectifier enough, then any overload on the DC side should also blow the primary side fuse.
Fusing individual drives isn't usually recommended, as if it fails for any reason, then you risk the drive being fried due it having no where to dump power from a moving motor to.
The drain resistor should simply connect across the capacitor terminals. Unless you have some reason to quickly dump power, you don't need to have it switched. The motor drivers themselves will quickly drain the capacitors with power removed.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Denford Triac VMC year 2000 motors spec
By suesi34e in forum Milling Machines, Builds & ConversionsReplies: 1Last Post: 17-11-2013, 11:44 PM -
Advice on spindle inverter spec
By badgerman in forum Spindles & Drive MotorsReplies: 12Last Post: 15-09-2013, 09:26 PM -
Hiwin linear blocks HGW 20 CC - what preload to spec?
By range3rrr in forum Rails, Guideways & BearingsReplies: 1Last Post: 24-08-2011, 11:44 PM -
FOR SALE: Servo Spec gearbox's ---- Any offer considered
By Jimmybristol in forum Items For SaleReplies: 11Last Post: 30-05-2011, 11:04 PM -
System spec and Mach3
By gorbo in forum Computer HardwareReplies: 5Last Post: 23-01-2011, 03:25 PM



Reply With Quote
Bookmarks