    Quote Originally Posted by m_c View Post
    If you're worried about not switching something back on, for the interlock, use a switch with an extra contact, or wire in an extra relay, and have it connected to an additional input, then set up the controller to prevent it from restarting until it sees the additional input, and flagging up if the interlock isn't closed.
    Isn't that just the same has what I said in post #5.?

  2. #2
    as an ex employee of www.emachcnc.com we used to use m3 to turn on spindle and m5 to turn it off, the output from the controller switched a relay, for added safety we supplied the inverter via a contactor, whose coil was switched via a key switch, as far as the HSE were concerned, as long as the facility to remove a tool ( key ) to make safe the spindle, it was deemed safe to handle.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. EMCO Spindle Control
    By Pete92 in forum Spindles & Drive Motors
    Replies: 1
    Last Post: 06-11-2013, 10:20 PM
  2. PCPPS B.O.B. - OK for spindle control?
    By birchy in forum Spindles & Drive Motors
    Replies: 4
    Last Post: 09-09-2013, 12:50 AM
  3. Spindle Speed Control
    By cncJim in forum Spindles & Drive Motors
    Replies: 15
    Last Post: 18-06-2013, 07:53 PM
  4. Replies: 2
    Last Post: 11-12-2012, 12:58 PM
  5. Help with spindle control
    By wizzy in forum Spindles & Drive Motors
    Replies: 4
    Last Post: 12-02-2011, 12:51 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •