    The alarm terminals don't output any power. It's an open collector output capable of switching 100mA at 30V.

    So you still need a relay as per John's suggestion to connect into to the Estop circuit, but you need to provide the power to the relay, then connect the relay to ground via the alarm terminals. You could also have the relay in circuit after the alarm terminals, but it's usually better practice to switch the ground side in electronics.

  2. The Following User Says Thank You to m_c For This Useful Post:


Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Leadshine website and AM882
    By EddyCurrent in forum General Electronics
    Replies: 12
    Last Post: 24-08-2018, 01:59 AM
  2. Need to slow down a signal due to Safe Torque Off alarm
    By corkcnc in forum General Electronics
    Replies: 0
    Last Post: 04-06-2014, 11:35 PM
  3. AM882 Alarm Circuit
    By Wobblycogs in forum General Electronics
    Replies: 8
    Last Post: 28-03-2014, 06:06 PM
  4. Output direct to machine
    By picyman in forum Vectric
    Replies: 4
    Last Post: 16-02-2014, 11:04 PM
  5. HPGL driver output
    By 2006Nobull in forum Computer Software
    Replies: 6
    Last Post: 07-10-2012, 08:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •