Either way of wiring in the relay would work. Your first diagram switched the high (positive) side, and your second switched the low (negative/gnd) side.
Only thing that threw me was the markings on your relays. Vcc is a supply voltage in electronics, whereas you've used it for the contacts.
Ricardoco is right that e-stop circuits should be fail safe. For the actual e-stop button circuit, the relay should be active when the e-stop circuit is not in stop condition, with the BOB e-stop wires going through a pair of NO (Normally Open) contacts. That way if anything fails, the machine stops.
With the drive alarm function, a truly failsafe method is not possible due to the fact the alarm only activates when there is a fault, so you need to implement a system that relies on relays/wiring working when there is a fault. This isn't quite as big an issue on the alarm funcion, as a failure to stop when a drive faults out isn't as major a safety issue. At worst two axis keep moving, while one sits still.
-
The Following User Says Thank You to m_c For This Useful Post:
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Leadshine website and AM882
By EddyCurrent in forum General ElectronicsReplies: 12Last Post: 24-08-2018, 01:59 AM -
Need to slow down a signal due to Safe Torque Off alarm
By corkcnc in forum General ElectronicsReplies: 0Last Post: 04-06-2014, 11:35 PM -
AM882 Alarm Circuit
By Wobblycogs in forum General ElectronicsReplies: 8Last Post: 28-03-2014, 06:06 PM -
Output direct to machine
By picyman in forum VectricReplies: 4Last Post: 16-02-2014, 11:04 PM -
HPGL driver output
By 2006Nobull in forum Computer SoftwareReplies: 6Last Post: 07-10-2012, 08:49 PM
Bookmarks