Hello Bill,
I can only echo what other people have said about your rebuild. It has been a great read prior to the, hopefully soon, delivery of a KL-1 I'm negotiating to buy.
In the mean time I have been reading about your VFD conversion, including the information and drawings from the Yahoo Hardinge Group.
If I may, I had a couple of questions about the VFD that have been confusing me.
Yourself and some other people use a 240v to 480v transformer to power the VFD.
From the information I can find about the Siemens MM150 you use, it appears to be a 240VAC Single Phase input device, and looking through general component suppliers (RS), the only 480VAC input VFD's are 3 phase inputs, and the single phase input VFD's are 240VAC.
I wondered what the reason for the transformer is, since I assume that you are still only getting a single phase output from the transformer, just at 480v ?
I wouldn't have thought you could feed a 480VAC single phase into a FVD designed for a 480VAC 3 phase input, can you ?
Yours Confused !
Paul.
-
24-02-2013 #2
Hi Paul,
No. The Siemens MM150 VFD I am using is the 1.5kW 500v three phase input version. It is fed from the single phase 415vac output of a step up transformer.the Siemens MM150 you use, it appears to be a 240VAC Single Phase input device,
All VFDs run on DC internally, so they do not really require more than one phase to work. High power ones have 3ph input because they need more current and it is easier (i.e. smaller, cheaper capacitors) to smooth the DC from a poly-phase input (like a single cylinder engine needs a bigger flywheel than a multi- cylinder engine) .
There is sufficient capacity in most VFDs to operate on a single phase input without causing any real problems (especially on a lathe with a low duty cycle operation).
Some VFDs have phase loss detection, which would prevent single phase operation, but most newer ones just sense DC bus ripple voltage so will operate fine on single phase input (they will still fault if excessively loaded).
Bill
-
25-02-2013 #3
Hi Bill,
Thanks for such a prompt reply.
That makes a lot more sense now.
I'm assuming that the risk is that since only one phase is being used to supply all the output power, that it is the rectifier diodes on the one input that risk being over-loaded - all the output power being derived from one phase set of rectifier diodes rather than three ?
Do you just leave two of the input phases disconnected ?
Using a 3 phase 415 input VFD makes the selection choice much larger and cheaper !
Many Thanks - I'll look into 415v 3ph VFD's now !
Regards
Paul.
-
27-02-2013 #4True, but since the rectifier diodes are usually integrated with the rest of the power devices, there's virtually no cost to the manufacturer to make the devices very robust (i.e. to use the same spec devices for the smallest and largest power VFD in a range).I'm assuming that the risk is that since only one phase is being used to supply all the output power, that it is the rectifier diodes on the one input that risk being over-loaded - all the output power being derived from one phase set of rectifier diodes rather than three ?
The only real issue is ripple current heating in the capacitors.
Bill
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
REBUILD: Hardinge HC rebuild
By northumbrian in forum Lathe Rebuild LogsReplies: 29Last Post: 21-02-2017, 12:07 PM -
Hardinge KL-1
By pauly45 in forum Conversion Build LogsReplies: 22Last Post: 18-10-2013, 07:31 PM -
WANTED: Hardinge hlv-h or Feeler 618
By cookie in forum Items WantedReplies: 1Last Post: 26-02-2011, 09:09 PM -
NEW MEMBER: Hardinge HLV-H Lathe
By Roger Williams in forum New Member IntroductionsReplies: 1Last Post: 25-08-2009, 01:56 PM -
Hardinge HLV-H manuals
By BillTodd in forum Milling Machines, Builds & ConversionsReplies: 13Last Post: 10-02-2009, 12:22 AM



Reply With Quote

Bookmarks