17-11-2013 #1
Good timing lads !
@silyavski, the temperature switch was already built into my spindle, it is closed normally and opens at high temperature.
@cncJim, see latest drawings
Here are my latest drawings
Features
---------
Strategy 1
* Emergency stop immediately signals VFD to stop and several seconds later (time to be assessed but possibly 6 seconds) delayed contacts of Guardmaster safety relay open to operate STO (Safe Torque Off) feature of VFD which disables control voltage and power semiconductors.
* Power removed from Stepper Drivers via Guardmaster safety relay and K1
* Stop command issued to Mach3 via K1 (even if Mach was still active the VFD and Stepper Drivers would still be disabled)
Strategy 2
* Stop signal sent to VFD via K3 relay
* Stop command issued to Mach3 via K3
* Enable (ENA) signal activated via Mach3 and BOB to disable stepper drivers
Strategy 3
Not implemented - same as Strategy 2
Strategy 4
* Stop signal sent to VFD via K4 relay
* FeedHold command issued to Mach3 via K4
* Enable (ENA) signal activated via Mach3 and BOB to disable stepper drivers
Strategy 5
Not implemented
Notes:
Strategy 3 could be implemented by incorporating a relay contact from K3 into K1 coil circuit however because all 4 contacts of K3 are being used another single contact relay would have to be connected in parallel with K3.
Strategy 5 could be implemented by removing the Pause push button and having only K4-4 contacts operational.
* A PAUSE push button has been added, this will stop the VFD and send a FeedHold signal to Mach3, to continue the ON (RESET) push button is pressed.
* A Charge Pump relay has been added to the Emergency Stop circuit this so the system can initiate an Emergency Stop if the software stops or communication is lost.
* If the Circuit Breaker for the Stepper Drivers trips then K1 will de-energise and send a STOP signal to Mach3.
* ENA signal now connected from BOB to all Stepper Drivers
( ** As yet I have not cobbled together the Charge Pump relay but I think a small 5v coil one will do the job as my BOB can source 20mA. **)
Relays K2,K3 and K4 are these
http://www.ebay.co.uk/itm/1set-Base-...item5d388b7d84Last edited by EddyCurrent; 18-11-2013 at 09:22 AM.
-
19-11-2013 #2
Good stuff EddyCurrent, I'm still working my way through your diagrams trying to fully understand :) - Do you have any provision for activating your estop circuit from the controlling software? I suppose the argument could be made that its not needed unless the pc a distance from the machine?
I have just acquired 10 of these from a control panel I stripped down (7x 24v and 3x 230v) which seem to be a similar spec to yours:-
Finder TYPE 55.34
The 5A rating, is that for the entire relay or for each contact?
There are also 4 contactors which I haven't taken out yet. Are there any practical/safety differences between a relay and a contactor?Last edited by cncJim; 19-11-2013 at 06:39 PM.
-
19-11-2013 #3
Yes that's what the Charge Pump relay is doing. The BOB is turning a 12khz signal from Mach3 into a 0 or 5vdc output, on my particular BOB the output of ENA is 0v when Mach3 is healthy and +5v dc when it stops.
Those look just right, I looked on Farnell and they appear to be 4 pole Change Over which is what you need if using my diagram, the 5A rating is for each contact.Last edited by EddyCurrent; 19-11-2013 at 09:39 PM.
-
19-11-2013 #4
-
19-11-2013 #5
With electrical systems there are generally two main circuits, the 'control circuit' and the 'power circuit'. Contactors are regarded as components of the power circuit whereas relays belong to the control circuit, it's mostly to do with the current carrying capacity and the ability to break that circuit without arcing or at least controlling the arcing. There are relays with positive guided contacts and these are for use in safety circuits, I have not come across equivalent contactors but that's not to say they don't exist. I'm not 100% on this but I think relays originated in communications areas such as telephone exchanges. Contactors can have auxilliary contacts fitted which in essence are relay equivalents and are used in the control circuits for those contactors.
Last edited by EddyCurrent; 19-11-2013 at 11:30 PM.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
traveling steady, turning 1/2 bar down over 10".
By graffian in forum Metalwork DiscussionReplies: 3Last Post: 08-05-2013, 07:59 PM -
NEW MEMBER: Hello all, finally ready to start a build log.
By Iwant1 in forum New Member IntroductionsReplies: 11Last Post: 25-12-2012, 06:03 PM -
eBay: Boxford 125 TCL Mach3 Ready
By rnr107 in forum Items On eBay UKReplies: 1Last Post: 25-07-2012, 07:29 AM -
Anyone have experience of ready made machines
By bogstandard in forum Milling Machines, Builds & ConversionsReplies: 9Last Post: 07-04-2010, 07:44 PM -
Windows 7 RTM Confirmed & Ready !
By Lee Roberts in forum Computer SoftwareReplies: 8Last Post: 29-07-2009, 03:33 PM
Bookmarks