    I'm going to guess it was one of the standard/non-rotary phase converters he used, and the motor has burnt out because you have to derate them when running on a static converter.

    What you can replace it with depends on how much starting torque is needed. You can get high starting torque single phase motors, but they are quite a bit more expensive (search for capacitor start motors).

  2. #2
    If it's 1400RPM, then it's most likely a 4-pole motor - the question is: have the manufacturers used a 4-pole for the extra torque or was it purely a speed related thing? Most single phase motors will have a capacitor start. Basically, the bigger the capacitor, the greater the starting torque.

    You'll probably need to match the motor frame size and mounting type, but I see no reason why a single phase motor can't be used. The other option is to go for a 3-phase motor but use a VFD (Variable Frequency Drive) inverter to drive it. You can get some decent single phase in/ three phase out drives nowadays for around £100. TEC motors are decent and usually a bit cheaper than the Italian ones. Another option is to get a used 3-phase motor from a scrapyard. They're usually good motors which have been removed from industrial machinery. More importantly, they're about £5 each and can be driven by a VFD...

  3. #3
    m_c's Avatar
    Lives in East Lothian, United Kingdom. Last Activity: 7 Hours Ago Forum Superstar, has done so much to help others, they deserve a medal. Has a total post count of 2,957. Received thanks 366 times, giving thanks to others 8 times.
    Capacitor start motors (I think officialy they should be called capacitor start/capacitor run) use a centrifugal switch to disconnect the start capacitor once upto speed, otherwise the motor will cook itself pretty quickly.

    Having said that, a 3phase and VFD is probably a more practical option. If a high startup load is involved, you might need to oversize the VFD a bit to give a bit more current for startup purposes.

  4. #4
    According to the data sheets the 0.75kw 3 phase 4 pole motor produces about 5.1Nm torque but you have to go to a 1.5kw single phase 4 pole motor for that same torque.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Replies: 2
    Last Post: 23-04-2014, 03:14 PM
  2. Big single phase servos and drivers
    By m_c in forum Stepper & Servo Motors
    Replies: 0
    Last Post: 04-09-2013, 01:18 AM
  3. Replies: 19
    Last Post: 21-08-2013, 11:20 PM
  4. Servo motor sizing?
    By gavztheouch in forum Stepper & Servo Motors
    Replies: 1
    Last Post: 18-04-2013, 11:40 PM
  5. convert 3 phase to single phase?
    By D-man in forum General Electronics
    Replies: 10
    Last Post: 06-04-2013, 12:16 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •